Using a Variac to heat a flexible rope heater

  • Thread starter Thread starter tribosonics
  • Start date Start date
  • Tags Tags
    Heat Heater Rope
AI Thread Summary
Using a variac rated at 4A to power a 240V flexible rope heater requires careful consideration, as the heater will draw 4.3 amps at full voltage. It is recommended to limit the variac output to about 90% of full voltage to avoid overloading. Safety precautions are crucial due to the risk of electrical shock; a designated area should be roped off to prevent accidental contact. Users must be aware of the dangers associated with improper use of electrical equipment, as highlighted by warnings from the manufacturer. Proper handling and caution are essential when conducting this experiment.
tribosonics
Messages
1
Reaction score
0
Hi,

I want to use a variac that I've got (4A rating) to power one of these:

http://www.omega.co.uk/ppt/pptsc.asp?ref=FGS_FGH_FWH&Nav=heam02

but a 240V version. The problem is I can't figure out if the variac that I've got has sufficient grunt to do it (without frying me, the variac or the heater).

Any suggestions?

Phil
 
Engineering news on Phys.org
tribosonics said:
Hi,

I want to use a variac that I've got (4A rating) to power one of these:

http://www.omega.co.uk/ppt/pptsc.asp?ref=FGS_FGH_FWH&Nav=heam02

but a 240V version. The problem is I can't figure out if the variac that I've got has sufficient grunt to do it (without frying me, the variac or the heater).

Any suggestions?

Phil
The 240 volt models will draw 4.3 amps at 240 volts, so you need to limit the voltage you use out of the variac to perhaps 90% of full voltage (220 volts).

This is a dangerous personnel hazard, even with the variac. Rope off an area around this expeiment so no one can accidentally touch it. I have seen people electrocuted before, so beware.
 
Bob S said:
This is a dangerous personnel hazard, even with the variac. Rope off an area around this expeiment so no one can accidentally touch it. I have seen people electrocuted before, so beware.

Yeah, and from the Omega website:

Omega said:
CAUTION AND WARNING!
Fire and electrical shock may result if products are used improperly or installed or used by non-qualified personnel. See inside back cover for additional warnings.
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...