Utilizing Fan Coil Unit return to fullfill fresh air requirements

AI Thread Summary
Utilizing a fan coil unit for fresh air requirements raises concerns about compliance with ASHRAE 62.1 standards and humidity control. The configuration is deemed inadequate for maintaining proper indoor air quality and is often seen as a shortcut. Constant-speed, cycling fans may lead to positive pressure buildup, potentially hindering fresh air supply. There is a need for guidelines on maintaining positive pressure in buildings to enhance indoor air quality. Overall, this approach is not recommended for effective ventilation and humidity management.
tj00889
Messages
6
Reaction score
1
TL;DR Summary
Hello,
I'm currently working on an HVAC Villa project in Dubai where the client has requested that he does not wish to pay for a dedicated fresh air fan to provide fresh air. He added that the common method of doing this in commercial projects in Dubai is to extend a fresh air duct from outside to the FCU return plenum as shown in the drawing. Can this provide sufficient control of how much fresh air will enter to be compliant with ASHRAE 62.1 and what problems can I expect.
Thank you very much
Schematic.PNG
 
  • Like
Likes russ_watters
Engineering news on Phys.org
Great question, with multiple facets/layers. I'll get back with more when I have more time, but yes you are right to be concerned about outside air/62.1 compliance. Also, this configuration will not adequately control humidity. It's a bad idea, but unfortunately a common shortcut.

Question for you: are the fans constant or variable speed? Always running or cycling?
 
Last edited:
russ_watters said:
Great question, with multiple facets/layers. I'll get back with more when I have more time, but yes you are right to be concerned about outside air/62.1 compliance. Also, this configuration will not adequately control humidity. It's a bad idea, but unfortunately a common shortcut.

Question for you: are the fans constant or variable speed? Always running or cycling?
The fans are constant speed and cycling.
What I am worried about is if the positive pressure buildup in the room would stop fresh air supply all together. There is also the issue that seeing as there is no way to maintain the building at positive pressure with this configuration, I was wondering if there is anything in ashrae i could use that states that maintaining the building at positive pressure is a requirement or at least a suggestion for better indoor air quality
 
How did you find PF?: Via Google search Hi, I have a vessel I 3D printed to investigate single bubble rise. The vessel has a 4 mm gap separated by acrylic panels. This is essentially my viewing chamber where I can record the bubble motion. The vessel is open to atmosphere. The bubble generation mechanism is composed of a syringe pump and glass capillary tube (Internal Diameter of 0.45 mm). I connect a 1/4” air line hose from the syringe to the capillary The bubble is formed at the tip...
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
I'd like to create a thread with links to 3-D Printer resources, including printers and software package suggestions. My motivations are selfish, as I have a 3-D printed project that I'm working on, and I'd like to buy a simple printer and use low cost software to make the first prototype. There are some previous threads about 3-D printing like this: https://www.physicsforums.com/threads/are-3d-printers-easy-to-use-yet.917489/ but none that address the overall topic (unless I've missed...
Back
Top