Voltage readings in 14-3 Romex connected to combo switch

  • Context: Electrical 
  • Thread starter Thread starter Stephen Tashi
  • Start date Start date
  • Tags Tags
    Switch Voltage
Click For Summary

Discussion Overview

The discussion revolves around voltage readings in a 14-3 Romex cable connected to a combination switch in a residential electrical circuit. Participants explore how the positions of the switches affect voltage measurements, particularly in relation to capacitive coupling and the implications of using different types of measuring devices.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant questions whether the voltage between the red and white wires in the 14-3 Romex should depend on the positions of both switches in the combination switch.
  • Another participant suggests that the observed voltage readings are not due to induced voltages but rather capacitive coupling within the cable.
  • It is noted that voltage readings from a "floating" circuit node can be ambiguous and that connecting the circuit to loads would yield more reliable readings.
  • A participant mentions that using a digital voltmeter, which has high input impedance, can result in significant voltage readings due to stray capacitance, while an analog meter would likely show little or no voltage under similar conditions.
  • Another participant adds that using a meter that loads the circuit could lead to different voltage readings.

Areas of Agreement / Disagreement

Participants generally agree that capacitive coupling is a likely explanation for the voltage readings, but there is no consensus on the implications of these readings or the best measuring practices.

Contextual Notes

Limitations include the lack of connection at one end of the 14-3 cable, which may affect current flow and voltage readings. The discussion also highlights the dependence on the type of measuring device used, which has not been resolved.

Who May Find This Useful

Individuals interested in electrical engineering, residential wiring, or those troubleshooting similar electrical circuit configurations may find this discussion relevant.

Stephen Tashi
Science Advisor
Homework Helper
Education Advisor
Messages
7,864
Reaction score
1,602
TL;DR
Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?
In a house (USA) there is "combination switch" ( e.g. https://www.acehardware.com/departm...utlets-and-plugs/switches/3235199?store=16359 ) containing 2 two-pole switches. [Edit: correction: 2 single pole switches]. The electrical diagram for the circuit ought to be the following:
comboSwitch.JPG


Should the voltage between R and W depend on whether switch S2 is open?

The input to the switch is the black wire from a 14-2 cable. The white wire of the 14-2 is connected to one end of the white wire of a 14-3 Romex cable. One end of the red wire of the 14-3 cable is connected to switch S1. One end of the black wire of the 14-3 cable is connected to switch S2. ( The 14-2 is an older type of cable that does not contain a ground wire.)

The other ends of the 14-3 cable are not yet connected to anything. When I measure the AC voltage from R to W with S2 open, I get about 120V or 0 V depending the position of S1. However, with S2 closed, I get about 60 V with S1 open. Does this have to do with induced voltages?

The 14-3 cable is about 20 ft long. I assembled a bench top version of the circuit using about 1 ft of 14-3 cable. With switch S1 open, I get about 3 V beween R and W with switch S2 open and about 6 V between R and W with switch S2 closed.
 
Last edited:
Physics news on Phys.org
Stephen Tashi said:
Summary:: Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?

Does this have to do with induced voltages?
Yes. Not induced, that implies magnetic field coupling due to current flow, which you don't have. It's really capacitive coupling inside the cable, most likely.

Voltage readings to a "floating" circuit node (i.e. disconnected from everything) are ambiguous. If you connected this configuration to whatever loads you intend, then you would get reliable (eg. 0) readings.
 
  • Like
Likes   Reactions: Stephen Tashi
Stephen Tashi said:
Summary:: Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?

However, with S2 closed, I get about 60 V with S1 open. Does this have to do with induced voltages?

With the 'other' end of the 14-3 not connected, there is not any current flow to create magnetic coupling. You are seeing capacitive coupling between the wires in the 14-3 cable.

You are probably using a digital voltmeter for the measurements. These have a very high input impedance so it doesn't take much stray capacitance for a significant voltage to show up.

Due to their much lower impedance, an older analog, moving coil, meter would read little or no voltage under the above conditions.

Cheers,
Tom
 
  • Like
Likes   Reactions: hutchphd and Stephen Tashi
If you use a meter that loads the circuit (ie a "wiggy") you will see very different readings.
 
  • Like
Likes   Reactions: Stephen Tashi

Similar threads

  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
Replies
6
Views
2K
  • · Replies 5 ·
Replies
5
Views
4K
  • · Replies 5 ·
Replies
5
Views
5K
  • · Replies 6 ·
Replies
6
Views
2K
Replies
14
Views
786
  • · Replies 29 ·
Replies
29
Views
2K
Replies
6
Views
3K