Voltage readings in 14-3 Romex connected to combo switch

  • Context: Electrical 
  • Thread starter Thread starter Stephen Tashi
  • Start date Start date
  • Tags Tags
    Switch Voltage
Click For Summary
SUMMARY

The discussion focuses on voltage readings in a 14-3 Romex cable connected to a combination switch, specifically how the voltage between the red and white wires is influenced by the positions of two single-pole switches. Measurements indicate that with switch S2 open, the voltage can vary significantly based on the position of switch S1, while closing S2 results in a capacitive coupling effect, showing around 60V with S1 open. The ambiguity in voltage readings is attributed to the high input impedance of digital voltmeters, which can detect stray capacitance, unlike analog meters that would show negligible voltage under similar conditions.

PREREQUISITES
  • Understanding of electrical circuits and switch configurations
  • Familiarity with 14-3 Romex cable wiring
  • Knowledge of voltage measurement techniques using digital and analog voltmeters
  • Concept of capacitive coupling in electrical systems
NEXT STEPS
  • Research the principles of capacitive coupling in electrical circuits
  • Learn about the differences between digital and analog voltmeters, including their impedance characteristics
  • Study the wiring and applications of 14-3 Romex cables in residential electrical systems
  • Explore troubleshooting techniques for ambiguous voltage readings in electrical circuits
USEFUL FOR

Electricians, electrical engineers, and DIY enthusiasts interested in understanding voltage behavior in residential wiring and troubleshooting electrical circuits.

Stephen Tashi
Science Advisor
Homework Helper
Education Advisor
Messages
7,864
Reaction score
1,602
TL;DR
Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?
In a house (USA) there is "combination switch" ( e.g. https://www.acehardware.com/departm...utlets-and-plugs/switches/3235199?store=16359 ) containing 2 two-pole switches. [Edit: correction: 2 single pole switches]. The electrical diagram for the circuit ought to be the following:
comboSwitch.JPG


Should the voltage between R and W depend on whether switch S2 is open?

The input to the switch is the black wire from a 14-2 cable. The white wire of the 14-2 is connected to one end of the white wire of a 14-3 Romex cable. One end of the red wire of the 14-3 cable is connected to switch S1. One end of the black wire of the 14-3 cable is connected to switch S2. ( The 14-2 is an older type of cable that does not contain a ground wire.)

The other ends of the 14-3 cable are not yet connected to anything. When I measure the AC voltage from R to W with S2 open, I get about 120V or 0 V depending the position of S1. However, with S2 closed, I get about 60 V with S1 open. Does this have to do with induced voltages?

The 14-3 cable is about 20 ft long. I assembled a bench top version of the circuit using about 1 ft of 14-3 cable. With switch S1 open, I get about 3 V beween R and W with switch S2 open and about 6 V between R and W with switch S2 closed.
 
Last edited:
Physics news on Phys.org
Stephen Tashi said:
Summary:: Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?

Does this have to do with induced voltages?
Yes. Not induced, that implies magnetic field coupling due to current flow, which you don't have. It's really capacitive coupling inside the cable, most likely.

Voltage readings to a "floating" circuit node (i.e. disconnected from everything) are ambiguous. If you connected this configuration to whatever loads you intend, then you would get reliable (eg. 0) readings.
 
  • Like
Likes   Reactions: Stephen Tashi
Stephen Tashi said:
Summary:: Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?

However, with S2 closed, I get about 60 V with S1 open. Does this have to do with induced voltages?

With the 'other' end of the 14-3 not connected, there is not any current flow to create magnetic coupling. You are seeing capacitive coupling between the wires in the 14-3 cable.

You are probably using a digital voltmeter for the measurements. These have a very high input impedance so it doesn't take much stray capacitance for a significant voltage to show up.

Due to their much lower impedance, an older analog, moving coil, meter would read little or no voltage under the above conditions.

Cheers,
Tom
 
  • Like
Likes   Reactions: hutchphd and Stephen Tashi
If you use a meter that loads the circuit (ie a "wiggy") you will see very different readings.
 
  • Like
Likes   Reactions: Stephen Tashi

Similar threads

  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
Replies
6
Views
2K
  • · Replies 5 ·
Replies
5
Views
4K
  • · Replies 5 ·
Replies
5
Views
5K
  • · Replies 6 ·
Replies
6
Views
2K
Replies
14
Views
702
  • · Replies 29 ·
Replies
29
Views
1K
Replies
6
Views
3K