The discussion centers on the behavior of voltage readings in a combination switch setup involving two single-pole switches. The circuit includes a 14-2 cable and a 14-3 Romex cable, with specific connections to switches S1 and S2. Voltage measurements between the red and white wires reveal varying results based on the states of the switches. When switch S2 is open, the voltage fluctuates between 120V and 0V depending on S1's position. However, with S2 closed, a reading of approximately 60V occurs with S1 open, raising questions about the cause of these readings.The phenomenon is attributed to capacitive coupling rather than induced voltages, as there is no current flow due to the disconnected end of the 14-3 cable. The use of a digital voltmeter, which has high input impedance, can lead to misleading voltage readings due to stray capacitance. In contrast, an analog meter would show little to no voltage under similar conditions.
Stephen Tashi
Science Advisor
Homework Helper
Education Advisor
Messages
7,864
Reaction score
1,602
TL;DR Summary
Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?
In a house (USA) there is "combination switch" ( e.g. https://www.acehardware.com/departm...utlets-and-plugs/switches/3235199?store=16359 ) containing 2 two-pole switches. [Edit: correction: 2 single pole switches]. The electrical diagram for the circuit ought to be the following:
comboSwitch.JPG


Should the voltage between R and W depend on whether switch S2 is open?

The input to the switch is the black wire from a 14-2 cable. The white wire of the 14-2 is connected to one end of the white wire of a 14-3 Romex cable. One end of the red wire of the 14-3 cable is connected to switch S1. One end of the black wire of the 14-3 cable is connected to switch S2. ( The 14-2 is an older type of cable that does not contain a ground wire.)

The other ends of the 14-3 cable are not yet connected to anything. When I measure the AC voltage from R to W with S2 open, I get about 120V or 0 V depending the position of S1. However, with S2 closed, I get about 60 V with S1 open. Does this have to do with induced voltages?

The 14-3 cable is about 20 ft long. I assembled a bench top version of the circuit using about 1 ft of 14-3 cable. With switch S1 open, I get about 3 V beween R and W with switch S2 open and about 6 V between R and W with switch S2 closed.
 
Last edited:
Physics news on Phys.org
Stephen Tashi said:
Summary:: Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?

Does this have to do with induced voltages?
Yes. Not induced, that implies magnetic field coupling due to current flow, which you don't have. It's really capacitive coupling inside the cable, most likely.

Voltage readings to a "floating" circuit node (i.e. disconnected from everything) are ambiguous. If you connected this configuration to whatever loads you intend, then you would get reliable (eg. 0) readings.
 
  • Like
Likes Stephen Tashi
Stephen Tashi said:
Summary:: Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?

However, with S2 closed, I get about 60 V with S1 open. Does this have to do with induced voltages?

With the 'other' end of the 14-3 not connected, there is not any current flow to create magnetic coupling. You are seeing capacitive coupling between the wires in the 14-3 cable.

You are probably using a digital voltmeter for the measurements. These have a very high input impedance so it doesn't take much stray capacitance for a significant voltage to show up.

Due to their much lower impedance, an older analog, moving coil, meter would read little or no voltage under the above conditions.

Cheers,
Tom
 
  • Like
Likes hutchphd and Stephen Tashi
If you use a meter that loads the circuit (ie a "wiggy") you will see very different readings.
 
  • Like
Likes Stephen Tashi
Three rabbits will be wintering in a 2m x 2m x 2m wooden hut. Outside temperature does not go below -30c (-22f) Planning to put a 50cm by 50cm 1mm thick stainless steel sheet on the floor of the hut (inside off course) My plan is to heat the sheet with a 50w PTC heater element https://fi.rsdelivers.com/product/dbk-enclosures/fg135600/dbk-enclosures-heating-element-75mm-50-w-100-240-v/dc/2995922?backToResults=1 Is this heater (50W) enough to keep the pad warm enough to sustain liquid...