Electrical Voltage readings in 14-3 Romex connected to combo switch

  • Thread starter Thread starter Stephen Tashi
  • Start date Start date
  • Tags Tags
    Switch Voltage
Click For Summary
The discussion centers on the behavior of voltage readings in a combination switch setup involving two single-pole switches. The circuit includes a 14-2 cable and a 14-3 Romex cable, with specific connections to switches S1 and S2. Voltage measurements between the red and white wires reveal varying results based on the states of the switches. When switch S2 is open, the voltage fluctuates between 120V and 0V depending on S1's position. However, with S2 closed, a reading of approximately 60V occurs with S1 open, raising questions about the cause of these readings.The phenomenon is attributed to capacitive coupling rather than induced voltages, as there is no current flow due to the disconnected end of the 14-3 cable. The use of a digital voltmeter, which has high input impedance, can lead to misleading voltage readings due to stray capacitance. In contrast, an analog meter would show little to no voltage under similar conditions.
Stephen Tashi
Science Advisor
Homework Helper
Education Advisor
Messages
7,864
Reaction score
1,602
TL;DR
Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?
In a house (USA) there is "combination switch" ( e.g. https://www.acehardware.com/departm...utlets-and-plugs/switches/3235199?store=16359 ) containing 2 two-pole switches. [Edit: correction: 2 single pole switches]. The electrical diagram for the circuit ought to be the following:
comboSwitch.JPG


Should the voltage between R and W depend on whether switch S2 is open?

The input to the switch is the black wire from a 14-2 cable. The white wire of the 14-2 is connected to one end of the white wire of a 14-3 Romex cable. One end of the red wire of the 14-3 cable is connected to switch S1. One end of the black wire of the 14-3 cable is connected to switch S2. ( The 14-2 is an older type of cable that does not contain a ground wire.)

The other ends of the 14-3 cable are not yet connected to anything. When I measure the AC voltage from R to W with S2 open, I get about 120V or 0 V depending the position of S1. However, with S2 closed, I get about 60 V with S1 open. Does this have to do with induced voltages?

The 14-3 cable is about 20 ft long. I assembled a bench top version of the circuit using about 1 ft of 14-3 cable. With switch S1 open, I get about 3 V beween R and W with switch S2 open and about 6 V between R and W with switch S2 closed.
 
Last edited:
Physics news on Phys.org
Stephen Tashi said:
Summary:: Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?

Does this have to do with induced voltages?
Yes. Not induced, that implies magnetic field coupling due to current flow, which you don't have. It's really capacitive coupling inside the cable, most likely.

Voltage readings to a "floating" circuit node (i.e. disconnected from everything) are ambiguous. If you connected this configuration to whatever loads you intend, then you would get reliable (eg. 0) readings.
 
  • Like
Likes Stephen Tashi
Stephen Tashi said:
Summary:: Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?

However, with S2 closed, I get about 60 V with S1 open. Does this have to do with induced voltages?

With the 'other' end of the 14-3 not connected, there is not any current flow to create magnetic coupling. You are seeing capacitive coupling between the wires in the 14-3 cable.

You are probably using a digital voltmeter for the measurements. These have a very high input impedance so it doesn't take much stray capacitance for a significant voltage to show up.

Due to their much lower impedance, an older analog, moving coil, meter would read little or no voltage under the above conditions.

Cheers,
Tom
 
  • Like
Likes hutchphd and Stephen Tashi
If you use a meter that loads the circuit (ie a "wiggy") you will see very different readings.
 
  • Like
Likes Stephen Tashi
The idea is to use water to shift the centre of gravity of the pendulum by a small amount. The pendulum rod will have a tube closed at the bottom and open at the top. A second similar tube will be mounted nearby and will act as a reservoir. The water will be transferred using a peristaltic pump driven by a stepper motor and will travel via a thin flexible silicon tube. A loop arrangement will minimise friction at the pendulum's fulcrum. The silicon tube will extend to the bottom of the...
Philips Hue was the very first provider of smart LED bulbs that can be controlled wirelessly. Over the years, as Philips sold ever improved models of smartbulbs, it became very difficult to identify exactly which model one of their bulbs is. Once I've installed a smart bulb, there is some additional information in the Hue app about the bulb model, but even then, I found that it requires information from both the app and from what's printed on the outside of bulb to be sure what the actual...
Some time ago I posted this Raspberry PI DIY Mass Spec using Raman Scattering. It's was something of a cumbersome project though, needing a 3D printer and special heat-resistant plastic giving of carcinogenic fumes during printing. To be blunt it was also not very mobile and interpreting the results was further cumbersome Recently though, I've been told that Arduino, and it's various sensor packages, has matured to the point where it's a usable alternative. Now I realize that a cigarette...