What are the different types of losses in a transformer?

  • Thread starter Thread starter shaiqbashir
  • Start date Start date
  • Tags Tags
    Transformer
AI Thread Summary
Transformers experience several types of losses, primarily categorized into core losses and ohmic losses. Core losses consist of hysteresis losses, which depend on voltage and frequency, and eddy current losses, which are proportional to the square of the voltage and independent of frequency. Ohmic losses occur in the copper windings due to resistance, calculated as I^2R for both primary and secondary coils. Additionally, stray losses arise from leakage fields inducing eddy currents in surrounding conductive materials. Understanding these losses is crucial for optimizing transformer efficiency and performance.
shaiqbashir
Messages
103
Reaction score
0
Hi Guys!

Well! I am studying transformer and i want to know about the following losses in a transformer:

1)Hysteresis Losses
2)Eddy Current Losses
3)Copper Losses
4)Stray Losses

please explain me the right concept. I have studied so much but I am just not getting the right concepts to understand these losses.

Thanks in advance
 
Engineering news on Phys.org
There are mainly two kinds of losses in a transformer,namely
(1)core loss.
(2)Ohmic loss.
1.Core loss:

These core losses in transformer consists of two components hysteresis loss and eddy current loss
i.e. core loss=hysteresis loss+eddy current loss.
hysteresis losses depends on applied voltage and its frequency
eddy current loss is proportional to squre of the applied votage and is independent of frequency f.
3.Ohmic loss:
when transformer is loadded ohmic losses(i^2*r)occurs in both the primary and secondary winding resisrances.
In addition to core loss the follwing loss has to be taken into consideration

Stray losses: Leakage fields present in the transformer induce eddy currents in conductors,tanks,channels,bolts etc. and these eddy currents give rise to stray losses.
 
Last edited:
CORE LOSSES:


I. the energy dissipated in the core due to hysterisis over one cycle is the area enclosed by the hysterisis loop:
E_{\mbox{per cycle}}=\oint B(H)dH,

where B and H are the magnetic field (flux density) and magnetizing intensity (or auxilliary field or just "H") present in the core. Physically, this loss is understood as the energy required to orient and reorient the magnetic domains in the ferromagnetic material, when the direction of the magnetic field changes due to the A.C. current. The rate of dissipation is basically the area enclosed by the curve times the frequency.

II. Eddy current is a consequence of faraday's law of voltage induction: when A.C. current is applied to the windings, this changing current results in a magnetic flux which "flows" through the core of the transformer-- this flux is proportional to the current, so it is also CHANGING in time. Time changing fluxes induce time changing electromotive forces. The induced emf's are loops which are essentially around the path of the flux in a cylindrical manner; since the core material (iron) is a conductor, the induced emf's will give rise to currents that swirl around the loop of the emf.

OHMIC LOSS:
This one is the easiest to understand-- The copper windings of the primary and secondary of the transformer are (obviously) conductors, so some energy will be dissipated in them. The copper wire of the primary and secondary will have total resistances of R_{P} and R_{S}; energy will dissipate in them at a rate of <br /> P_{\mbox{ohmic}}=I_{P}^2R_{P}+I_{S}^2R_{S}.
Note that the resistances of the wires depend on frequency to some extent-- higher frequency, higher resistance (skin effect).

STRAY LOSSES:
Since the world is not "ideal" air has some finite albeit small magnetic permeability \mu_{\mbox{air}}\approx\mu_{0}=4\pi \times 10^-^7\mbox{H/m}, which means it presents a LARGE reluctance to magnetic flux, so some of the flux will "leak" out of the core of the transformer. As a model, you can view the air and core as two reluctances (the magnetic analog of resistnace) in "parallel". The smaller reluctance - the path formed by the iron core - will take most of the flux, since the larger reluctance - the air - is not infinite in value some flux loops out and passes through it. If there are conducting materials in the path you can again have losses from the farady induction in those materials.


Hope this helps. If you aren't familiar with the concept of reluctance, I suggest searching magnetic circuits concepts, also search for the full equivalent circuit model of the transformer. All of these losses, can be modeled to an approximation with inductances and resistances.
 
Last edited:
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Back
Top