Vitina
- 23
- 9
I would like to add that this is called a grounded Y system.
The neutral carries any imbalance current.
The size of the conductors and direct connections to lighting indicates low voltage (240 volts to ground, 400 volts 3 phase) system. Ground conductor is separate from neutral because
1. Unbalanced currents will develop a voltage on neutral (this is usually small, about 0-10 volts but can have a relatively large current associated with it).
2. The ground dissipates accumulated static charge and protects wires under it from lightning.
That is 5 wires, 4 insulated (phase 1,2,3, and neutral), (and the separate ground over the top).
Oh, and the neutral is grounded but usually only at the transformer end so as not to carry power current.
The neutral carries any imbalance current.
The size of the conductors and direct connections to lighting indicates low voltage (240 volts to ground, 400 volts 3 phase) system. Ground conductor is separate from neutral because
1. Unbalanced currents will develop a voltage on neutral (this is usually small, about 0-10 volts but can have a relatively large current associated with it).
2. The ground dissipates accumulated static charge and protects wires under it from lightning.
That is 5 wires, 4 insulated (phase 1,2,3, and neutral), (and the separate ground over the top).
Oh, and the neutral is grounded but usually only at the transformer end so as not to carry power current.