A PTO like what
@anorlunda suggests is a good way to go using a truck engine as power source. I'm having a hard time envisioning fitting the required number of off-the-shelf alternators under the hood, and belting them to the engine shaft. If not a truck engine-driven PTO then an externally driven genset may be the best option.
1.
Captain Mike said:
Mounting the generator on the outside is NOT an option. No-one will be able to hear anyone order anything.
Is a low noise requirement the only one nixing having the generator on the outside?
If so, perhaps a noise reduction enclosure brings an external generator back into the game. This isn't an endorsement, but went poking around, and found a manufacturer,
Zombie Box, that serves this market. The Duromax XP12000EH generator is rated for 74 dB or less of noise production. Their X-Large noise enclosure provides a minimum 16 dB reduction.
2.
Captain Mike said:
I DID have a gasoline/propane generator that had what they said an "internal failure" and it burned down half of the old vehicle.
Is it possible to find out the nature of the "internal failure"? Was it on the fuel system/engine side, or an electrical issue?
About how many hours of run time did the generator have? The manual calls for various inspections and component replacements on 150 and 300 run hour intervals, which is roughly every 3 to 6 weeks for an 8 hour operating day.
3.
Captain Mike said:
Chest freezer, freezerless fridge, hotbox, steamtable, heatlamp, hoodvent, fridge/freezer, sandwich table cooler, the small amount of power for the water heaters electrics (It's fuel is LP), lights, and 2 water pumps (one of which is gray water and won't be used when we are serving so I didn't count that. It works out to roughly 9,375 W with everything running peak (that is with the chest freezer in the higher amp "startup" and the hood vent motor on high which on our last vehicle we didn't need it on high)
12000W peak/9500W continuous rating applies to generator operation using gasoline for fuel, and derates to 10200W peak/8075W continuous running on propane.
Electrical loading was close to generator rating, and may have exceeded it upon occasion.
4.
Captain Mike said:
The generator did have a low voltage trip.
Was this added later? No mention of a low voltage trip is made in the XP12000EH operator manual, it isn't shown in the electrical schematic, and none of the photos show a low voltage trip indicator.
Can't say for certain, but with a generator running close to full output the possibility exists it could run hunky-dory so long as only one or perhaps two of the fridge/freezer compressor motors turned on at the same time, but if all three turned on at the same time for voltage to drop enough to prevent one or more of the motors from coming up to speed, continue to pull high startup current, and (without undervolt protection) cause generator and/or motor failure.