I admit to being beyond my area of expertise in Transmission and Distribution(T&D). It is a different environment from in plant distribution and there are nuances of which i am at best only marginally aware.
I was taught some fifty five years ago that T&D used "neutral" for the small residual unbalance currents and to intercept lightning. Since it needn't carry much current it can be small, and since it's near ground potential it needn't be insulated. Most but not all transmission lines I've seen in the years since indeed have that fourth conductor .and it's usually run above the power conductors .
So i am not asserting that the T&D neutral serves the same purpose as a NEC "Bonding Conductor"
only that the laws of Kirchoff and Ohm will prevail.
I am aware that T&D relay folks use means far more sophisticated than simple overcurrent to detect faults, and that's necessary because of the distances involved.
@Svein 's comments about ungrounded systems i am sure have basis in analytical methods for detecting power system faults.
Here's a 357 page book on the subject. I'm no expert, just a fellow who's aware of how little
he i know of it. .
http://www.gegridsolutions.com/multilin/notes/artsci/artsci.pdf
I simply do not want this thread to convey to beginners the mistaken idea that power systems are ungrounded hence ground fault currents would be small.