The discussion revolves around calculating current in a power transmission cable with given values of power, voltage, and resistance. Users highlight inconsistencies in the provided values, noting that using either P=VI or V=IR leads to different results, suggesting that one or more values may be incorrect. The correct approach to find the current is to use P=VI, which gives a current of 2A, assuming the power is delivered to a load. The conversation emphasizes the ambiguity in the problem, particularly regarding whether the power and voltage refer to the source or the load, leading to multiple potential interpretations and answers. Ultimately, clarity in the problem statement is essential for accurate calculations.
liangtp
Messages
2
Reaction score
0
Hi,

In a power transmission cable, the power, P=24W, Voltage=12V, the resistance of the cable, R=4 ohm.

What is the current that flows in this cable? Shall I use P=VI or V=IR to calculate the current?
Both seems to give different answers.

Thanks
 
Physics news on Phys.org
I'm fairly certain that this situation is impossible fundamentally. You should get the same answer for both.
 
One of your given values seems to be incorrect.

If the voltage and resistance are correct, then:
P = V2/R = 12V2/4Ω = 36W

If power and voltage are correct:
R = V2/P = 122/24W = 6Ω

If power and resistance are correct:
V = √(P*R) = √(24W*4Ω) = 9.8V
 
Last edited:
Thanks all for your response.

Agreed with both of you.
Somehow my gut instinct told me that the question I had was somehow flawed.

Thanks again.
 
liangtp said:
Hi,

In a power transmission cable, the power, P=24W, Voltage=12V, the resistance of the cable, R=4 ohm.

What is the current that flows in this cable? Shall I use P=VI or V=IR to calculate the current?
Both seems to give different answers.

Thanks

In this type of situation, or power system, it is generally meant,
the power source is a 12V source and it is delivering 24W power.
In such case, for current flowing from the source, use
P = VI
Then I = 2A.



Probably a load of 2 ohms is missing from the problem, which makes total resistance 6 ohm.
You shouldn't use V=IR unless the problem clearly indicates 12V is dropped in the resistance R.
 
It's also useful to remember that P = V2/R (alternatively P = I2R)

You can of course derive both expressions.
You can see immediately that 12*12/4 is not 24 so the question is nonsense.
 
Neandethal00 said:
Probably a load of 2 ohms is missing from the problem, which makes total resistance 6 ohm.
I think that is the solution to the issue.
A power transmission cable is supposed to transmit something - using it as short circuit (with just the cable resistance) would be a bit pointless anyway.

=> Current I=24W/12V=2A

The cable will get P=I^2*R = 4A^2*4Ω=16W of heat, and the load will receive 4A^2*2Ω=8W.
 
The question is not clear enough to be sure you can get the right answer.

For example..

The power is 24W but is that the transmitted power or the power dissipated in the load?
The voltage is 12V but is that the voltage at the source or the load?

So that's at least four possible right answers!

In most situations a transmission system has to be designed to suit the load not the source. For example in a PC the motherboard needs defined voltages (with a tollerance) measured at the motherboard not at the power supply end of the wiring loom.

So one valid answer would be to assume the load needs 12V delivered and will draw 24W.

That would suggest the current through the load is 24W/12V = 2A.
If the the cable resistance is 4 Ohms the source voltage needs to be 12+2*4 = 20V.
The power delivered by the source would be 20V * 2A = 40W.

but as I said that's just one of a number of possible answers that could be argued are correct given the problem statement is so loose.
 