Why do Current Transformer cores have different knee point voltages?

AI Thread Summary
The knee point voltage of current transformer (CT) cores is critical for determining their performance, particularly in balancing primary and secondary currents. The knee point is where a small increase in voltage results in a significant increase in current, but this specification is not directly applicable to CTs as it is for inductors and voltage transformers. The selection of core material and design must ensure that the magnetizing current remains small compared to the measured current, which affects accuracy and saturation limits. Different classes of CTs, such as metering and protection CTs, have varying accuracy requirements and saturation points based on their intended applications. Understanding these specifications is essential for testing and designing effective current transformers.
Manoj Sahu
Messages
54
Reaction score
1
I have to test a Current transformer. I read knee point is a point at which 10% increase in voltage leads to 50% increase in current. As there are different classes of current transformer (cores), how it is decided what/how much will be the knee point voltage of that core.
 
Engineering news on Phys.org
Manoj Sahu said:
I have to test a Current transformer.
Then you will need to know the specifications of that current transformer. What accuracy must it meet, over what range of line current and frequency. The secondary load specification will be an important parameter. You must test those characteristics rather than design a new transformer core.

Manoj Sahu said:
I read knee point is a point at which 10% increase in voltage leads to 50% increase in current.
That knee specification of the core is applicable to inductors and voltage transformers, but it is not directly applicable to current transformers.

A current transformer operates with an independent primary current. Part of the primary current produces the magnetising flux for the core while the remaining primary current must be balanced by the secondary ampere turns. It is therefore critical that the secondary load be specified and controlled.

The selection of core material for a current transformer requires the magnetising current that generates the flux be kept small compared to the current being measured. See; Chap 16, Transformer and Inductor Design Handbook, 2011, Colonel Wm T McLyman.
https://coefs.uncc.edu/mnoras/files/2013/03/Transformer-and-Inductor-Design-Handbook_Chapter_16.pdf

See also; https://www.eiseverywhere.com/file_uploads/1b3d32ecaf287ed7ce68ae5799836a96_CTTestingTheory.pdf
 
Last edited:
  • Like
Likes jim hardy and Manoj Sahu
Baluncore said:
Then you will need to know the specifications of that current transformer. What accuracy must it meet, over what range of line current and frequency. The secondary load specification will be an important parameter. You must test those characteristics rather than design a new transformer core.That knee specification of the core is applicable to inductors and voltage transformers, but it is not directly applicable to current transformers.

A current transformer operates with an independent primary current. Part of the primary current produces the magnetising flux for the core while the remaining primary current must be balanced by the secondary ampere turns. It is therefore critical that the secondary load be specified and controlled.

The selection of core material for a current transformer requires the magnetising current that generates the flux be kept small compared to the current being measured. See; Chap 16, Transformer and Inductor Design Handbook, 2011, Colonel Wm T McLyman.
https://coefs.uncc.edu/mnoras/files/2013/03/Transformer-and-Inductor-Design-Handbook_Chapter_16.pdf

See also; https://www.eiseverywhere.com/file_uploads/1b3d32ecaf287ed7ce68ae5799836a96_CTTestingTheory.pdf
Thank you
 
Manoj Sahu said:
how it is decided what/how much will be the knee point voltage of that core.

I sense possible confusion on my part as to the wording of your question.
Did you really mean "decided" ? as by the transformer designer ?
or
Measured ? as by a student in an EE lab class ?

That's two different questions.

The student in a lab class should think for a minute about the current transformer .
It's just two windings on a core, and that's no different from a voltage transformer
so the current transformer will transform voltage just as happily as it transforms current.

That said,
The fundamental difference between a Voltage transformer and a Current transformer is how we use it.
With a current transformer we control primary current not voltage,
whereas with a voltage transformer we control primary voltage and let primary current fall where it pleases. Unloaded, that's its magnetizing current.

So to me, a transformer is a transformer
A current transformer is just a transformer with an excellent core that requires very little magnetizing current.

So, a student can apply small voltage, measure current that results, and plot current versus volts on graph paper.
That's called an "Excitation Curve" for the transformer irrespective of how it will be used.
The knee will be readily apparent on the excitation curve. .
The student should be very careful in applying voltage to not go very much beyond the knee
because if he "saturates" the core he can ruin the insulation and wreck the transformer.

A designer would decide what accuracy he needs and follow the process in that most excellent link provided by @Baluncore .

old jim
 
Last edited:
  • Like
Likes Manoj Sahu and Baluncore
Thanks Jim
I meant calculated/decided by the designer.
If a current transformer is saturated, does it act like permanent magnet.
jim hardy said:
I sense possible confusion on my part as to the wording of your question.
Did you really mean "decided" ? as by the transformer designer ?
or
Measured ? as by a student in an EE lab class ?

That's two different questions.

The student in a lab class should think for a minute about the current transformer .
It's just two windings on a core, and that's no different from a voltage transformer
so the current transformer will transform voltage just as happily as it transforms current.

That said,
The fundamental difference between a Voltage transformer and a Current transformer is how we use it.
With a current transformer we control primary current not voltage,
whereas with a voltage transformer we control primary voltage and let primary current fall where it pleases. Unloaded, that's its magnetizing current.

So to me, a transformer is a transformer
A current transformer is just a transformer with an excellent core that requires very little magnetizing current.

So, a student can apply small voltage, measure current that results, and plot current versus volts on graph paper.
That's called an "Excitation Curve" for the transformer irrespective of how it will be used.
The knee will be readily apparent on the excitation curve. .
The student should be very careful in applying voltage to not go very much beyond the knee
because if he "saturates" the core he can ruin the insulation and wreck the transformer.

A designer would decide what accuracy he needs and follow the process in that most excellent link provided by @Baluncore .

old jim
 
Manoj Sahu said:
I meant calculated/decided by the designer.

Thanks for clarifying ! As i suspected the misunderstanding was mine .

Manoj Sahu said:
If a current transformer is saturated, does it act like permanent magnet.

Not necessarily, though it can become magnetized (look up remanence) which leaves it some distance up the B-H curve and will make it inaccurate.
If that happens, one should demagnetize it by applying gradually decreasing AC current to it.

The danger of driving a current transformer into saturation with AC current is that flux will change from maximum positive to maximum negative over just a fraction of a line cycle;
meaning ##\frac{Δflux}{Δtime}## is very large
and such a rapid rate of change of flux induces far larger than normal voltage in the windings;
which might pierce the insulation,
in addition to leaving it magnetized

old jim
 
  • Like
Likes Manoj Sahu
jim hardy said:
Thanks for clarifying ! As i suspected the misunderstanding was mine .
Not necessarily, though it can become magnetized (look up remanence) which leaves it some distance up the B-H curve and will make it inaccurate.
If that happens, one should demagnetize it by applying gradually decreasing AC current to it.

The danger of driving a current transformer into saturation with AC current is that flux will change from maximum positive to maximum negative over just a fraction of a line cycle;
meaning ##\frac{Δflux}{Δtime}## is very large
and such a rapid rate of change of flux induces far larger than normal voltage in the windings;
which might pierce the insulation,
in addition to leaving it magnetized

old jim
While doing the knee point test, I injected voltage upto 1500 V in a current transformer having knee point voltage 750V @ 30mA. The test was performed using Omicron's CPC 100 and it also had option to demagnetize.
IMG_20190106_115512.jpeg
 

Attachments

  • IMG_20190106_115512.jpeg
    IMG_20190106_115512.jpeg
    38.9 KB · Views: 845
Manoj Sahu said:
I injected voltage upto 1500 V in a current transformer having knee point voltage 750V @ 30mA.
Interesting - i never saw such an instrument...
in my day we'd have used analog meters and graph paper .i can't make out the display
milliamps on horizontal, volts vertical ? Knee where i circled in red?

upload_2019-1-7_7-58-12.png
 

Attachments

  • upload_2019-1-7_7-58-12.png
    upload_2019-1-7_7-58-12.png
    49.6 KB · Views: 1,109
jim hardy said:
Interesting - i never saw such an instrument...
in my day we'd have used analog meters and graph paper .i can't make out the display
milliamps on horizontal, volts vertical ? Knee where i circled in red?

View attachment 236920
Yes. Exactly. Voltage on y -axis and Current on x -axis. You have marked at the right place. The result was as follows
Knee point voltage -804V
Current - 5.508 mA
 
  • #10
The Knee is just the Saturation point, viewed by exciting the Secondary ( instrument side) - so really the question is how does the designer determine the saturation limit of a transformer. So different objectives ( Price, weight, size, cost, window,) are balanced against the technical limitations. Since the window types only have One primary turn, the secondary turns is set, limiting the options of the designer. Core type ( material) and size ( think cross sectional area) - are the biggest factors.

The different classes have different objectives - a metering CT needs to be very accurate at all of the operating point up to the rated current - usually this is with a relatively low burden load ( the meters). A protection CT really has a much bigger ask - as the accuracy must at least be known and understood at 10, 20 or more times nominal current - this may be through a number or variety of protective relays ( although the multi function digital protective relay helps greatly with this issue). In basic applications, like a feeder with only Over-current, GF protection the same CT may be used for basic metering ( usually non-revenue).
 
  • Like
Likes Manoj Sahu
  • #11
Windadct said:
The Knee is just the Saturation point, viewed by exciting the Secondary ( instrument side) - so really the question is how does the designer determine the saturation limit of a transformer. So different objectives ( Price, weight, size, cost, window,) are balanced against the technical limitations. Since the window types only have One primary turn, the secondary turns is set, limiting the options of the designer. Core type ( material) and size ( think cross sectional area) - are the biggest factors.

The different classes have different objectives - a metering CT needs to be very accurate at all of the operating point up to the rated current - usually this is with a relatively low burden load ( the meters). A protection CT really has a much bigger ask - as the accuracy must at least be known and understood at 10, 20 or more times nominal current - this may be through a number or variety of protective relays ( although the multi function digital protective relay helps greatly with this issue). In basic applications, like a feeder with only Over-current, GF protection the same CT may be used for basic metering ( usually non-revenue).
As you said metering core needs to be accurate all the time and protection core accuracy must be at least known or 10- 20 nominal current, is this the reason protection core is having larger saturation point.
I have a CT in which there are 4 core.
The first core is used for metering whereas the other cores are used for protection and differential protection.
 
  • #12
You have a CT with 4 core - or 4 windings? Ether way that seems odd ... - do you have a link to a Datasheet?

But - yes the protection one I would expect to have higher saturation
 
  • #13
Windadct said:
You have a CT with 4 core - or 4 windings? Ether way that seems odd ... - do you have a link to a Datasheet?

But - yes the protection one I would expect to have higher saturation
It has 4 core marked as
1S1-1S2-1S3 400-300/1A
2S1-2S2
3S1-3S2
4S1-4S2
 
  • #14
Ah.. a https://electrical-engineering-portal.com/understanding-the-ratios-of-magnetic-hv-instrument-current-transformers
 
  • #15
Windadct said:
Ah.. a https://electrical-engineering-portal.com/understanding-the-ratios-of-magnetic-hv-instrument-current-transformers
Exactly. It's installed in a 66kV Gas Insulated Substation
 
  • #16
Here - the cost of adding the CT is high so it is worth using a more complex one...
 
  • Like
Likes Manoj Sahu
  • #17
Knee point of the CT at BH curve depends on the following parameters.

  1. The Fault current of the electrical network
  2. The burden of the CT (Rct)
The designer ask the above information before designing the PS(Special protection) class CT.The information is sought to design the CT accordingly to system requirement in order to avoid the saturation of the CT in case of the fault. The CT saturation will cause no tripping of the circuit breaker and severe damage may takes place.

The Knee point voltage of the CTs installed for particular installation will differ from other electrical installation because different electrical installations have different fault current. The fault current depends on the rating of the transformer installed, number of HT and LT motor installed etc. The protection class and PS class Cts have less knee point voltage as compared to the PS class CT. The metering class CT saturate at lower knee point voltage. The protection class CT has more KPV and it does not saturate in case of the fault.
 
Last edited: