ZigZag transformer and harmonics

AI Thread Summary
Zigzag connections can be utilized on the secondary side of transformers to mitigate triplen harmonics from propagating through the power system. The cancellation of triplen harmonics occurs because they are in phase, preventing them from inducing currents in the primary winding. However, for this cancellation to be effective, the triplen harmonics must be real currents rather than just mathematical representations. The presence of additional harmonics, such as the 5th, complicates this cancellation, as the waveform would not be purely 3rd harmonic. Understanding these nuances is crucial for effective harmonic mitigation strategies in power systems.
KraakeCrest
Messages
18
Reaction score
2
Hi again,

Can/are zig zag connections used on the secondary side to avoid triplen harmonics flowing further up the power system? Let's say 3rd harmonics are flowing up the power system from some loads connected to phases a,b,c and the neutral. Since 3rd harmonic are all in phase, the ampere-turn created will cancel in a zig zag connection and thus not couple to the primary and further up the power system?

This pdf: http://static.schneider-electric.us...ansformers/Harmonic Mitigating/7400DB0301.pdf says on page 12 and 13:
"With all of the triplen harmonics in phase with each other, by vector analysis, the triplen harmonic currents produce ampere-turn fluxes that cancel each other such that no currents are induced in the primary winding. For this to work, the triplen harmonics must be real currents and not mere mathematical identities derived by the Fourier Transformation."

The last sentence in bold kind of confuses me.
zig.png
 
Engineering news on Phys.org
Nice post @jim hardy , so from that post if I understand correctly, you can use a zig zag connection as secondary in a transformer to prevent triplen harmonics from coupling magnetically back to the primary.

But I am still alittle confused about the sentence in the PDF: "For this to work, the triplen harmonics must be real currents and not mere mathematical identities derived by the Fourier Transformation."

So if the current caused by the load contains fundamental + 3rd AND 5th harmonic, this would not work because the waveform is not a pure 3rd harmonic waveform? Hmm..
 
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Hello dear reader, a brief introduction: Some 4 years ago someone started developing health related issues, apparently due to exposure to RF & ELF related frequencies and/or fields (Magnetic). This is currently becoming known as EHS. (Electromagnetic hypersensitivity is a claimed sensitivity to electromagnetic fields, to which adverse symptoms are attributed.) She experiences a deep burning sensation throughout her entire body, leaving her in pain and exhausted after a pulse has occurred...