In synchronous generator, how does armature reaction cause a 'drop' ? How is it different from the leakage reactance of stator windings? I can't visualize it..Please help..
Last edited by a moderator:
The discussion revolves around the concept of armature reaction in synchronous generators, specifically how it causes a 'drop' in generated voltage and its distinction from leakage reactance in stator windings. Participants explore visualization techniques, mathematical relationships, and the implications of power factor on terminal voltage.
Participants express differing views on the nature of armature reaction and synchronous reactance, with no consensus reached on the exact implications of the 'drop' or the relationship between generated voltage and synchronous reactance.
Participants reference various assumptions about power factor and the mathematical relationships between voltage and flux, but these assumptions remain unresolved and depend on specific definitions and contexts.
In case of unity pf, armature amp-turns neither add to nor subtract from the field amp turns. They just distort the field amp turns. And if they enhance or weaken field flux at other power factors, this will reduce the 'generated emf'. What I read in book was 'part of generated emf is used to overcome the armature reaction reactance'. That means generated emf is constant. But with reactive loads, its not true because some part of armature amp turns enhance or weaken the field amp turns. Is there anything similar to 'back emf' that is induced in the armature windings due to armature reaction? What does the term 'drop' mean in this context? Is it reduction in the generated voltage or a part of it being used to overcome synchronous reactance? If it is later, how does that reactance work??jim hardy said:The way to visualize it is to freeze-frame your thinking. Stop the rotor with its pole centered underneath a phase winding and think of it as DC.
Armature amp-turns will either aid or oppose field amp-turns.
So they'll add to or subtract from field, affecting terminal volts just as if they were an internal impedance
Look up "Synchronous Impedance"
Armature reaction and synchronous reactance are two names for the same thing, and reflect two ways of thinking about it.cnh1995 said:Is it reduction in the generated voltage or a part of it being used to overcome synchronous reactance? If it is later, how does that reactance work??