The discussion centers on optimizing secondary circulator and piping design for a heating system with two boilers, each handling 75% of the heating load. The boiler manufacturer recommends a specific formula for calculating secondary flow based on temperature rise, which raises questions about the balance between flow rate and temperature. Participants debate whether to prioritize higher temperatures with less water flow or to use more water at lower temperatures for efficiency. A compromise temperature rise, such as 40 or 50 degrees Fahrenheit, is suggested as a potential solution. The conversation highlights the need for careful consideration of system design to achieve optimal performance.
Artman
Messages
1,506
Reaction score
40
I would like to get some opinions on secondary circulator and piping design for heating system.

System Description:

Two (2) boilers each one is 75% of building total heating load. Each with a secondary circulator pumping to a manifold into a primary loop. The return piping comes from a second manifold adjacent to to supply manifold.

Primary loop with two (2) parallel circulators moving the heating water 100% of the heating load using a 20 deg F TD to the building and through the equipment.

Okay, the boiler manufacturer suggests the formula:

Gross Output BTUH/(Temp Rise x 500) = Secondary gpm

Temp Rise = 230 deg F - Return Water Temp

I know that the boiler can handle higher flows than will be obtained through this formula (with a 70 deg Temp Rise and a 515,000 btuh boiler I only get 14.7 gpm).

So which is better, use less water at higher temperature, or use more water at lower, closer to system, temperature? Or is it best to figure a compromise and go with that? Say a 40 deg F or 50 deg F temperature rise in the boiler?
 
Engineering news on Phys.org
Thread 'Where is my curb stop?'
My water meter is submerged under water for about 95% of the year. Today I took a photograph of the inside of my water meter box because today is one of the rare days that my water meter is not submerged in water. Here is the photograph that I took of my water meter with the cover on: Here is a photograph I took of my water meter with the cover off: I edited the photograph to draw a red circle around a knob on my water meter. Is that knob that I drew a red circle around my meter...
Hi all, i have some questions about the tesla turbine: is a tesla turbine more efficient than a steam engine or a stirling engine ? about the discs of the tesla turbine warping because of the high speed rotations; does running the engine on a lower speed solve that or will the discs warp anyway after time ? what is the difference in efficiency between the tesla turbine running at high speed and running it at a lower speed ( as fast as possible but low enough to not warp de discs) and: i...