xJuggleboy said:
Well here is the information I have to deal with.
1. The room is 10x10x10 and it is empty
2. The air being circulated taken from the room put into the AC and then put back into the room at the rate of 200 cubic feet/min
3. BTU/hr changes with time over a 3min cycle from about 2000BTU/hr to 5000BTU/hr
4. the room starts at 95F and it needs to get to 70
5. Humidity is around 20% at 95F
I don't know any of the calculations to get anywhere with this... Any help is apreciated.
George
Get out a psychometric chart and look up 20% Relative Humidity and 95°F. Follow it over to find your humidity ratio (i think), its omega either way. That will give you a mass ratio of water to air in the room. Now, cool the air down to 70° by moving straight left until you hit the saturation line, then follow that line down to 70°F. The point that you hit the saturation line is called the Dew Point, any cooling beyond that point will result in condensation.
Anyways, the initial and at the final point, if you trace those points "northwest" you will be able to find enthalpy. From there I would think you could just get your difference in enthalpy and will then proceed to use your energy balance.
OK OK, I just remembered that I have my Thermo Book here at work. Here's what you do:
First, write a Dry Air and Water mass balance
m(a1) = m(a2) = m(a)
m(a1)w(1) = m(a2)w(2) + m(w)
where terms in () are subscripts and a is air, w is water, and w is omega equals the humidity ratio in kg water/kg dry air gotten from the psychometric chart (sorry, if anyone wants to Latex this, they are more than welcome)
from the water balance you get m(w) = m(a)[w(1) - w(2)]
also note that all m's and Q's are mass and heat flow respectively, not just mass
Plugging into energy balance, we get:
Qout = m(a)[h1 - h2] - m(w)h(w)
*where h1 and h2 are from the psychometric chart, and h(w) js h(f) at your final temperature
So, get your chart out and get h's, omegas and specific volumes for both points.
m(a) mass flow of air = V1/v1 (V is volume flow)
m(w) = m(a)*(w1-w2)
Qout(flow) = m(a)[h1-h2] - m(w)h(w) and this gives you units of btu/min
Then I would guess you take the Btu of your AC, divided by that to give you units of minutes. I apologize for this being unclear and probably making no sense, but maybe you'll get a couple of tidbits outta it that will help you solve the problem.