I have been advised by my thermostat manufacturer that I need to reduce the voltage to prevent the O/B terminal on my thermostat from blowing again. The current voltage reading to power my thermostat is 28 volts and it needs to be closer to 24.
The current voltage reading to power my thermostat is 28 volts and it needs to be closer to 24. I assume this is possible with resisters, but I don't know where to begin. If possible what type of resistor do I need to buy? Thanks.
28 volts sounds suspicious to me. 24 volts is industry standard in this country.
There is a step-down transformer on your furnace that makes 24 volts for the thermostat.
It might be designed for 120 volt, 240 volt, or 208 volt input.
IF your transformer is made for 208 volts input and your furnace feeds it 240 volts, it'll put out about 27.8 volts instead of 24.
The transformer will also run hot to the touch.
Watch this video, pay special attention to the last minute, and then look at your furnace:
Make sure you have the right transformer in your furnace and it's set to the right tap. A 208 volt transformer operated at 240 will burn up in a few seasons.
The transformers cost about twenty bucks at my local hardware store.
http://www.grainger.com/Grainger/ecatalog/N-1z0dnhq
Don't mess around with resistors - fix it right.
Because Murphy's Law says a shortcut will ALWAYS cause you trouble , and at at the worst possible time.
old jim