What Are the Functional Differences Between AC22A and AC23A Isolator Operations?

  • Thread starter Thread starter nisham
  • Start date Start date
AI Thread Summary
AC22A and AC23A isolators differ primarily in their operational capabilities, with AC23A designed for more demanding applications involving highly inductive loads. The AC23A operation can handle lower power factors compared to AC22A, indicating its robustness for motor switching. Differences in contact size, material, and arc quenching mechanisms also contribute to their distinct functionalities. Manufacturers may assign multiple duty ratings to devices, allowing for flexibility in current ratings based on application requirements. Understanding these differences is crucial for selecting the appropriate isolator for specific electrical tasks.
nisham
Messages
2
Reaction score
0
Dears,

Can anyone brief what is the operation functionality of AC23A operation of isolators & what is the difference between AC22A & AC23A operation.
 
Engineering news on Phys.org
It would seem it's just a difference in ratings, AC23 being robust enough for more highly inductive loads.

http://www.hevacomphelp.com/ELEC/1pdf/MCP/0001.PDF
DEFINITIONS OF UTILIZATION
CATEGORY
AC20A Connecting and disconnecting
under no load condition.
AC21A Switching of resistive loads
including moderate overloads.
AC22A Switching of mixed resistive
and inductive loads including
moderate overloads.
AC23A Switching of motor, or other



Was that the question?
There'll be differences in contact size & material, and in the arc quenching apparatus.

This link gives power factor of 65% for AC22, 35% for AC23
http://www.gil-lec.co.uk/custom/upload/pdfs/circuit%20protection/Hager_Isolators_Switches.pdf

and suggests that a given switch may be used for more severe duty at reduced current
Manufacturers may assign more than one AC duty rating to their
devices. For example an AC22 switch can be given a lower
current rating when assigned to AC23 duty. Manufacturers may
also assign a maximum kW power rating for motors or a kVAr
reactive power rating for capacitors.


If you're looking for construction details , i'd take apart a few from different manufacturers to see how they get around one another's patents.
 
Last edited:
Thank you, even i have the same information as you have told. i would like to know what makes the AC23A duty to give a different current rating than other duty. Also what is the theoretical reason behind introducing such different duties in isolators.
 
nisham said:
Thank you, even i have the same information as you have told. i would like to know what makes the AC23A duty to give a different current rating than other duty. Also what is the theoretical reahttp://www.gil-lec.co.uk/custom/upload/pdfs/circuit%20protection/Hager_Isolators_Switches.pdfson behind introducing such different duties in isolators.


again, http://www.gil-lec.co.uk/custom/upload/pdfs/circuit%20protection/Hager_Isolators_Switches.pdf
Common types of defined switching category:
• 20 Connecting & disconnecting under no load.
• 21 Switching of resistive loads.
• 22 Switching of mixed resistive & inductive loads.
• 23 Switching of highly inductive loads.

Have you ever played with inductors and noticed how the make an arc when you interrupt current?

That is rough service for a contact - it must be made from something that resists arc welding.

e = l di/dt
 
Last edited by a moderator:
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...