Calculating Rafter Size for Douglas Fir-Larch
  • Thread starter Thread starter raiderUM
To determine the required rafter size for a roof span of 16 feet using Douglas fir-larch, the live load is 20 psf and the dead load is 15 psf. The maximum bending moment (M) is calculated as 2240 lb-ft, leading to a required section modulus (S) of 26.88 in³ for No. 1 grade and 29.87 in³ for No. 2 grade lumber. Both grades can be satisfied with 2x12 rafters, which meet the necessary structural requirements. Understanding the maximum bending moment allows for direct calculation of stress without needing to evaluate displacement. The discussion confirms that 2x12 rafters are adequate for this application.
raiderUM
Rafters are to be used on 24in centers for a roof span of 16ft. Live load is 20psf (without snow) and the dead load is 15psf, including the weight of the rafters. Find the rafter size required for Douglas fir-larch of No 1 grade and No 2 grade, based on bending stress
S= M/Fb
I don't know the Moment though? so I don't know where to start on this problem
S= M/Fb
It looks like the length of your beam is 16 ft, and the beam has a uniform load distribution along its length. Each beam supports a 2 ft width of roof. First find the weight supported per unit length of each beam (rafter). It probably would be reasonable to assume that each beam is simply supported at its ends. So determine the vertical shear force as a function of position along the beam (assuming that each end supports half the weight), and then integrate the bending moment subject to the boundary condition that the moments on the ends are both equal to zero. Calculate the displacement distribution next (based on the assumed cross sectional dimensions of the rafters, possibly using commercially available dimensions). This will allow you to get the local radius of curvature, and then the bending strain on the outside of the bend. This will give you the bending stress on the outside of the bend. Look up the tensile strength of Douglas fir larch, and compare this with your calculated tensile stress. If the tensile stress exceeds the tensile strength, choose a more robust commercial cross section.
Alternatively, to save some steps, once you determine the max moment of a simply supported beam under a uniformly distributed load, use your formula to determine S and then cross sections of available timber that yield that minimum value.
So the Live load is just Area(LL)=Area(DL), which equals 1120.
So M=WL/8 and V=W/2
M=2240
V=560
No 1 lumber Fb=1000
No 2 lumber Fb=900
S=M/Fb
2240(12)/1000 = 26.88 in^3
2240(12)/900 = 29.87 in^3
Which the table says 2x12 in both lumber sizes will cover it
Yes. This is an excellent point. Once you know the maximum bending moment, you don't need to solve for the downward displacement. You can get the maximum stress at the outside of the bend directly from the bending moment, knowing the cross section of the beam.
And the 2 x 12's look good!