Advice on circuit drawing

3 replies · 2K views · last reply
ismat143
Messages
10
Reaction score
0
Please See the drawing and Advise...
 
Attachments
  • Wiring diagram of a 3-phase motor starter: 3 ~ power supply feeds a 30 Amps MCB, then a 25 Amps contactor (LC1D25 Schneider) with A1/A2 220 volts coil supply, a LRD 22 Schneider overload relay set 16-24 amps, and a 7.5 KW 15-16 amps motor, with a 220 volts on/off switch on the auxiliary contacts.
    Overload relay.jpg
    33.6 KB · Views: 486
Overload - is just that - too much load on the motor, this is typically a long time ( relative to Short circuit issues) the OL Relay is configured for this case,, e.g. 150% of full load for 60 Seconds - etc.

A short circuit - is a fault, and the MCB is set up to protect for these cases, for example 5 to 10 x the Full load current, and this typically will trip in short ( 0.1 to 0.5 Sec after the Current is detected) or Instantaneous (as soon as the current is detected) -

The two device are protection for different types of problems.

Google Coordinated Motor Protection - that will probably be helpful.