Alternator Field Winding Question

AI Thread Summary
The discussion revolves around a 1979 Sencenbaugh wind generator with a 3-phase alternator that requires field winding excitation. The user is trying to deliver 60 watts to the field winding but is limited to approximately 30 watts due to a measured resistance of 6.5 Ohms. The user plans to connect the field winding directly to a 12-volt battery bank without regulation, raising concerns about potential overloading. Suggestions include using a manual switch to disconnect the field winding when not in use and considering a car regulator to manage the power supply. The user confirms that the alternator is functioning correctly, producing increasing voltage with RPM.
doubledipsoon
Messages
2
Reaction score
0
I
GOPR0229 (Small).JPG
have an older 12 volt battery-charging 1979 Sencenbaugh wind generator that I am testing. It has an 3 phase alternator with a field winding that must be excited, as opposed to the newer "permanent magnet" alternators. The manual says that 60 watts maximum should go to the field winding. According to theory, amps= watts over volts, so the amps to the field winding should be 60watts (the desired wattage to the field winding)/13.5 volts (battery bank at full charge). So the amps comes out to 4.4 amps. I just measured the Ohms off of the 2 field winding wires, and it came out to 6.5 Ohms, which allows only 30 watts to the field windings. So the big question is, how can I deliver 60 watts to my field winding? By the way, I won't be regulating the wattage to the field winding- I intend to keep 60 watts continually hooked up to the winding. I'm not an electrical engineer, I am self-taught, so I hope I'm thinking this out correctly. Thanks.
 
Engineering news on Phys.org
doubledipsoon said:
The manual says that 60 watts maximum should go to the field winding.
The key word in that specification is maximum. Generator output is typically controlled by varying the field current. If you can get the desired output power at a lower field current you are ahead of the game. Go for it.

Out of curiousity, you state:
doubledipsoon said:
I intend to keep 60 watts continually hooked up to the winding.
Where are those watts coming from? Why not just use them to charge the battery directly?

Cheers,
Tom
 
Hi Tom, the watts are coming from a battery bank that the wind generator alternator will be charging...Since the measured ohms off the field winding is 6.60, the watts delivered to the field windings is about 30 watts (watts = amps x ohms). So increasing the wattage isn't possible because of the resistence (ohms) in the wiring of the field winding won't allow any wattage above 30 watts- this is what I've concluded...I went ahead and hooked up the field winding to my 12 volt battery bank (13.5 volts), hooked up the 3 phase alternator to a DC rectifier, spun the alternator, and the volt meter registered 1, 2, 3...10 volts with increasing rpm (I could only spin it at about 120 rpm This alternator puts out 14 volts max at about 275 rpm. I think it's working fine, right? PS: At this point, I'm not going to regulate the field winding, but am willing to figure out how)
 
I agree it seems to be working OK.
I suggest at least a manual switch to disconnect the field from the battery bank when not in use.
An appropriate regulator would be one one from a car. And they disconnect from the battery until the alternator exceed the battery voltage. They are readily available, even at a junkyard if there is one close by.

Have Fun! (You will certainly get a workout cranking that thing.)
Tom
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...

Similar threads

Back
Top