Answering a Question on Three Impedances & Neutral Wire Current

AI Thread Summary
The discussion focuses on the method for calculating the neutral wire current in a star-connected system derived from a delta configuration with three impedances. The proposed method involves calculating the admittances, phase voltages, and new phase currents, but some participants suggest that it may be overly complex. An alternative approach is recommended, which involves transforming delta impedances to star impedances using specific formulas, followed by calculating line currents and the neutral current. There is also a mention of potential issues with symmetry in phase voltages and the need for additional data to apply the Millman theorem effectively. Overall, the conversation highlights the complexity of the calculations and the importance of clarity in the methodology.
nothing909
Messages
168
Reaction score
4
I just want to know if my method is correct in answer a question like this...

Three impedances z1=(2-j5), z2=(3+j4) and z3=(8+j0) are connected in delta to a 3 phase, 400v 50Hz supply.

1. Find the three line currents Ia, Ib and Ic
2. Find the S,P and Q and power factor for the load
3. If the nodes are now connected in star with a neutral connected, find the current in the neutral wire.

I'm on question 3 and I just want to know if this is the correct method to work it out:

1. Work out Yan, Ybn and Ycn.
2. Work out Vn'n using the equation Vn'n=(VanYan)(VbnYbn)(VcnYcn)/Yan+Ybn+Ycn
3. Work out the new phase voltages by doing Van'=Van-Vn'n , Vbn'=Vbn-Vn'n , Vcn'=Vcn-Vn'n
4. Work out the new phase currents by doing Ian'=Van'/Zan' , Ibn'=Vbn'/Zbn' , Icn'=Vcn'/Zcn'
5. Add all the new phase currents up and that'll give me the current in the neutral?

Is that the correct method to work it out? Have I did a step wrong or missed anything out?
 
Physics news on Phys.org
That looks way to complicated. You get three complex amplitudes for current, you can add them (don't forget the phase shift between the three lines), that gives the total current and its phase.
 
  • Like
Likes Babadag
I agree with mfb: it is a hard work with complex numbers. In my opinion you have to start by transfigure the delta into star using simple formulae as:
If delta impedances are:
Z12=R12+jX12; Z23=R23+jX23; Z31=R31+jX31 and star impedance are:
Z1=R1+jX1; Z2=R2+jX2; Z3=R3+jX3 then:
Z1=Z12*Z31/(Z12+Z23+Z31)
Z2=Z23*Z12/(Z12+Z23+Z31)
Z3=Z23*Z31/(Z12+Z23+Z31)
Now Yan=1/Z1 Ybn=1/Z2 Ycn=1/Z3
Van=V<0,Vbn=V<-120,Vcn=V<-240 V=400/SQRT(3)=241V[approx.]
 
In question 3, it is a star.
 
As usually-for me-I took the answers as questions. I am sorry! :nb)
So, from the beginning:
Question1: Find the three line currents Ia, Ib and Ic.
Transfigure delta to star and calculate Ia=Van/(Ra+jXa) [typical]
Where Van=V<0,Vbn=V<-120,Vcn=V<-240
[I presume the phase voltages are symmetric.]
In my opinion, Ia has to be: Ia=30.86+j62.7 A -for instance.
Q 2: Find the S,P and Q and power factor for the load.
S=Van*Ia*+Vbn*Ib*+Vcn*Ic* where Ia*=Ia conjugated [If Ia=IaRE+jIaIM then I*=IaRE-jIaIM].
P=RE(S); Q=IM(S)
Q 3: If the nodes are now connected in star with a neutral connected, find the current in the neutral wire.
Iastar=Van/Zab; Ibstar=Vbn/Zbc; Icstar=Vcn/Zca
Io[neutral]=Iastar+Ibstar+Icstar
In my opinion, Io has to be: Io=-44.36+j59.29 A -for instance.
 
It is something wrong, still. Actually, Io=- (Iastar+Ibstar+Icstar) then 44.36-j59.29 A:H
 
Now I saw the post title:
“Millman problem”. It is not Millman theorem that I followed.
However, sorry, another correction(!):
In the delta connection the currents are to be calculating from the relation:
Ia=Iab-Ica=Vab/Zab-Vca/Zca and the phase voltage Va=Ia*Za. Only Vab, Vbc, Vca are symmetric.
The neutral is not in the center and then Va, Vb and Vc [absolute values] are not symmetrical.
 
In my opinion, in order to calculate the currents using Millman theorem a lot of data are missing. See[for instance]:

http://www.elect.mrt.ac.lk/EE201_3phase_sym_comp.pdf

para. Unbalanced three phase systems

For instance Zneutral, Zsource,Zline are missing.

If we could consider all these as zero then E1=Van,E2=Vbn,E3=Vcn and Vnn'=0.
 
Back