Build a Solar-Powered Pool Pump: What You Need to Know

  • Thread starter Thread starter booter10ca
  • Start date Start date
  • Tags Tags
    Build Pump
AI Thread Summary
A 5W solar panel is insufficient to directly power a pool pump, which typically requires more energy, especially for starting. To utilize the 5W panel, it can be used to charge a battery, which then powers a suitable inverter for the pump. The required power depends on the pump's horsepower; for instance, a 0.5 HP pump may need around 1 kVA peak for starting. Storing energy in a lead-acid battery and using a DC brush or brushless DC motor can be more efficient. Overall, careful planning of the system's components is essential for effective operation.
booter10ca
Messages
3
Reaction score
0
hey
i have a 5W pv panel and was wondering if i could build some sort of circuit to run my pool pump? was wondering what i would need ... any thoughts would be appreciated
 
Engineering news on Phys.org
Probably more than 5W.
 
Like skeptic said, I think you'd be hard-pressed to run your pump off 5W.

However, you could always use that 5W solar cell as a circuit to power a circuit that enables your pump.
 
thats what I am looking to do, i know 5w isn't enough but if there is some sort of circuit i can construct to harness the power in battery cells or some other form is what I am looking to try and do
 
Start by determining the HP required by your pump. IF it is say 0.5 HP, you will probably need 1 kVA peak for starting volt-amps in a 0.5 HP induction motor. Store the energy from the panel in a lead-acid battery, and use a 1 kVA inverter. The average power will depend on the duty cycle of the pump. You can probably get 10 watts per square foot for charging a battery system, or ≈0.1 kilowatt-hours per day per square foot. Use an inverter to get 60 Hz power from a battery. You might be better off with a dc brush motor or a BLDC (brushless dc) motor, because the starting VA requirement is less.

Bob S
 
Bob S said:
Start by determining the HP required by your pump. IF it is say 0.5 HP, you will probably need 1 kVA peak for starting volt-amps in a 0.5 HP induction motor. Store the energy from the panel in a lead-acid battery, and use a 1 kVA inverter. The average power will depend on the duty cycle of the pump. You can probably get 10 watts per square foot for charging a battery system, or ≈0.1 kilowatt-hours per day per square foot. Use an inverter to get 60 Hz power from a battery. You might be better off with a dc brush motor or a BLDC (brushless dc) motor, because the starting VA requirement is less.

Bob S

Thanks alot
 
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
Thread 'How Does Jaguar's 1980s V12 Dual Coil Ignition System Enhance Spark Strength?'
I have come across a dual coil ignition system as used by Jaguar on their V12 in the 1980's. It uses two ignition coils with their primary windings wired in parallel. The primary coil has its secondary winding wired to the distributor and then to the spark plugs as is standard practice. However, the auxiliary coil has it secondary winding output sealed off. The purpose of the system was to provide a stronger spark to the plugs, always a difficult task with the very short dwell time of a...
Back
Top