To calculate the room temperature at an outside temperature of 0 C, the flow rate of water through the radiator is crucial, as only 40% of the intended flow is currently achieved. The water temperature entering the radiator adjusts based on the outside temperature, which complicates the calculations. With a reduced flow rate, the leaving water temperature drops significantly, leading to inadequate heating. Without sufficient data on the flow rate and specific heat calculations, determining the exact room temperature is challenging. Ultimately, the room temperature should ideally match the design condition, but the current setup may not achieve that due to flow restrictions.
TSN79
Messages
422
Reaction score
0
A room has a need for 2000W for an outside temp of -20 C. A radiator with this capacity is installed and receives water at 90 C, which exits at 70 C. But because of some error only 40% of the intended water amount flows through the radiator. The water temp delivered to the radiator is adjustet according to the outside temp, and is 60,5 C when outside temp is 0 C. What will the temp in the room be at an outside temp of 0 C ?

What I don't get is how to incorporate the fact that the water delivered to the radiator is adjustet according to the outside temp. How do I put this into my calculations?
 
Engineering news on Phys.org
This question is just bad. It doesn't provide anywhere near enough data and it's poorly framed.
 
Agreed. I think you will need at least a flow rate of the water, not just 40% of original flow rate. Given that you have a flow rate, you can find heat flow based on
Q(dot) = m(dot)Cp(T2-T1)
If the change in temperature is being changed constantly according to the outside temp, I assume some smart guy here could set up an integral or something...I'm not sure where to start based on the information given though.
 
I work in English units and I am not sure of the conversions, but here is a start:

Gpm = btuh/((EWT - LWT) * Specific Heat of Water * 60 * 8.33)

6800 btuh /((194-158) * 1 * 60 * 8.33) = .38 Gpm

40% of that would be about .15 Gpm

This flow rate will lower the leaving water temp to 103 deg F giving a 91 deg F Temp Difference (EWT-LWT).

The water temp entering when the outside air is 0 deg C is 141 Deg F - 91 deg F = 50 Deg F. Which is crap. Better get that flow restriction cleared or you'll crack your boiler.

Or are we to assume that the water system has been calibrated to give us the same loss due to reduced Delta T as the room will lose? Thus reducing the temperature difference. This would be common for an automatic outdoor reset system, but I don't think we have suffiecient data to determine the room temperature other than to say it should be the same as the design condition. The water temp changes not the room temp.
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...