Cooling Tower Sizing for 20 MW Power Plant in Weymouth, England

  • Thread starter Thread starter Harkaran Singh
  • Start date Start date
  • Tags Tags
    Cooling Sizing
AI Thread Summary
Cooling towers are being considered for a 20 MW power plant in Weymouth, England, to efficiently manage heat rejection from the system. The required temperature drop for the working fluid is from 30°C to 19°C, with local wet bulb temperatures around 9°C and high humidity levels. Calculations for the cooling tower's size, mass flow rates, and make-up water are needed, and resources such as a design guide and cooling tower calculators have been suggested. There is also a discussion about utilizing waste heat for other processes, such as greenhouse operations, to enhance efficiency. Engaging with companies that specialize in cooling tower design is recommended for tailored solutions.
Harkaran Singh
Messages
7
Reaction score
0
Hi guys,

I have question regarding cooling towers. I have been asked to check if cooling towers would be efficient and economical to cooling system for a power plant to be installed in Weymouth, England.

As per my calculations, heat to be rejected (in the condenser) from the system is 20 MW.
I'm not familiar with cooling towers and I need help calculating (very roughly) the size of the tower required, parasitic loads, mass flow rate of water and air and quantity of make-up water?

Heat energy to be rejected= 20 MW
Temp of working fluid in the condenser has to be dropped from 30 deg C to 19 deg C
Wet bulb temperature of the area is 9 deg C
Avg temperature of area 14 - 16 deg C
Relative humidity is 85 - 90 %

Any advice would be highly appreciated.
 
Engineering news on Phys.org
Not my field but it seems a shame to be wasting 20MW these days. Got room for some green houses?

http://www.queensu.ca/gazette/content/waste-heat-could-be-harnessed-growing-tomatoes
http://www.gfsa.com/events/greenhouse-to-utilize-co2-waste-heat-from-adjacent-ethanol-plant/
 
CWatters said:
Not my field but it seems a shame to be wasting 20MW these days. Got room for some green houses?

http://www.queensu.ca/gazette/content/waste-heat-could-be-harnessed-growing-tomatoes
http://www.gfsa.com/events/greenhouse-to-utilize-co2-waste-heat-from-adjacent-ethanol-plant/
Yes, I agree its a waste. I'm urging the people involved to use this heat in other processes at the site.
Area is a major concern here and that is the reason why I'm interested in the area the cooling tower would occupy
 
As I said it's not my field but I found a "rule of thumb" design guide from 1981 that I suppose might help. Not SI units though.

http://www.osti.gov/scitech/servlets/purl/5281927/

It also looks like there are companies producing calculators for their cooling tower products. I think I'd contact one or two that design these for a living to see what they would recommend. They would probably do most of the work for you.
 
  • Informative
  • Like
Likes Tom.G and Harkaran Singh
CWatters said:
As I said it's not my field but I found a "rule of thumb" design guide from 1981 that I suppose might help. Not SI units though.

http://www.osti.gov/scitech/servlets/purl/5281927/

It also looks like there are companies producing calculators for their cooling tower products. I think I'd contact one or two that design these for a living to see what they would recommend. They would probably do most of the work for you.
This is really helpful. Thank you :D
 
That will be smart choice to introduce Cooling Water Towers with Calculator for quick note of issues
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...