Correcting power factor without affecting active power.......

Click For Summary

Discussion Overview

The discussion revolves around the concept of correcting power factor without affecting active power in electrical systems, particularly in the context of AC power analysis and practical applications such as power supplies. Participants explore the relationships between voltage, current, active power, and reactive power, as well as the implications of power factor correction techniques.

Discussion Character

  • Exploratory
  • Technical explanation
  • Conceptual clarification
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • Some participants suggest that when correcting power factor, the current must change while the voltage is often considered constant.
  • Others argue that while voltage magnitude remains unchanged, the phase angle may vary, impacting the relationship between voltage and current.
  • A participant references Steinmetz's concept of impedance as a combination of resistance and reactance, noting that reactive power affects the phase shift between voltage and current.
  • One participant raises a concern about whether changing reactive power to correct power factor would lead to changes in current magnitude, questioning how this balances the active power formula.
  • Another participant provides a practical example involving a PC power supply, illustrating how power factor correction reduces current while maintaining active power, emphasizing the role of power factor in this context.
  • Some participants express confusion and seek clarification on the implications of power factor correction and its effects on current and voltage.

Areas of Agreement / Disagreement

Participants generally agree that power factor correction involves changes to reactive power and may affect current, but there is no consensus on the specifics of how these changes interact with active power. Multiple competing views remain regarding the implications of these corrections.

Contextual Notes

Participants reference specific articles for further understanding, indicating that there may be limitations in their current grasp of the concepts discussed. The discussion also highlights the complexity of the relationships between active power, reactive power, and power factor.

Who May Find This Useful

This discussion may be useful for individuals interested in electrical engineering, particularly those studying AC power systems, power factor correction techniques, and practical applications in electronics.

Voltageisntreal
Messages
18
Reaction score
5
When correcting power factor without affecting active power, wouldn't the current and voltage of the system have to change due to

Active power =VrmsIrmscos(theta), where cos(theta) is the power factor?
 
Engineering news on Phys.org
Most cases the voltage can be considered as given, so what changes is the current.
 
  • Like
Likes   Reactions: Voltageisntreal
  • Like
Likes   Reactions: Voltageisntreal
anorlunda said:
@Rive is right considering voltage magnitude, but the phase angle might change.

@Voltageisntreal , welcome to PF.

You might understand better after reading these two PF Insights articles.
https://www.physicsforums.com/insights/ac-power-analysis-part-1-basics/
https://www.physicsforums.com/insights/ac-power-analysis-part-2-network-analysis/

Hello to you too and thanks :D.

I'm not sure if I understand better now or not :p.

Steinmetz said, if I percieve correctly from the article, that z=A+jB, where jB is the phase shift. I've always just seen imaginary power as a phase shift between voltage and current in AC, where j is 90 degrees. Essentially, voltage is applied and then electromagnetic energy lags or leads it depending on whether the imaginary power is positive or negative which comes down to how capacitors and inductors act in AC.

My issue was that with a transformer in which I want to correct the power factor , but I want to keep active power the same, then you change reactive/imaginary power to get the result- yes. You do that by changing the phase angle indirectly by adding a capacitance or inductance.

I thought then, however, would that not result in a change in the current (as Rive said) in terms of it's magnitude to balance the formula: VIcos(theta)= Active Power?

I now feel, from the article, that because of this shift due to the change in reactive power-- V and I do change at instantaneous points because of the shift--- however, the rms remains the same and the average active power is therefore the same?

If so that does make more sense and thank you for you help :).
 
Let's take a simple example. If the PSU in your PC draws 460W, that would mean 2A at 230V.
Of course, PC power supplies has power factor correction these days. Without correction that PSU would draw 575VA (not W, but VA!), in case the power factor // cos(theta) is 0.8.
Since the voltage is the same 230V, it would mean 2.5A current.

So, we can say that in this case the PFC reduced the current to 2A from 2.5A, with the effective power remaining 460W. The very meaning of the PFC is that you modify the cos(theta) from 0.8 to 1 (so theta will change).

PS.: In PC PSUs the correction is done with electronics these days, not with transformers or simple additional inductive/capacitive elements.
 
  • Like
Likes   Reactions: Voltageisntreal
Rive said:
Let's take a simple example. If the PSU in your PC draws 460W, that would mean 2A at 230V.
Of course, PC power supplies has power factor correction these days. Without correction that PSU would draw 575VA (not W, but VA!), in case the power factor // cos(theta) is 0.8.
Since the voltage is the same 230V, it would mean 2.5A current.

So, we can say that in this case the PFC reduced the current to 2A from 2.5A, with the effective power remaining 460W. The very meaning of the PFC is that you modify the cos(theta) from 0.8 to 1 (so theta will change).

PS.: In PC PSUs the correction is done with electronics these days, not with transformers or simple additional inductive/capacitive elements.

I see, I had gotten confused :o! Tyvm :3 :D, I understand now. It does reduce the current, which it would have to because rms is average anyway so the shift wouldn't have affected it.<3.
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K
Replies
2
Views
2K
Replies
12
Views
3K
  • · Replies 31 ·
2
Replies
31
Views
3K
  • · Replies 4 ·
Replies
4
Views
1K
Replies
11
Views
3K