Current of delta 3 phase balanced power

  • Thread starter Thread starter david90
  • Start date Start date
AI Thread Summary
The discussion focuses on the calculation of L1's current in a delta 3-phase balanced power system using Kirchhoff's Current Law (KCL). Participants debate whether the equation should be IR-IB or IR+IB, considering the current directions and voltage polarities. It is noted that the choice of current polarities is arbitrary but must be consistently applied once defined. The conversation emphasizes that current and voltage polarities do not need to align, allowing for flexibility in definitions. Ultimately, clarity in the chosen conventions is crucial for accurate calculations.
david90
Messages
311
Reaction score
2
Hi,

Regarding the picture below, the author calculates L1's current with KCL equation IR-IB = L1. Why is the KCL equation not IR+IB = L1 if the voltage of phase B and Phase R at one point during their cycle can be both positive (Assume positive voltage means current go toward the node)? If Phase B and Phase R voltage are positive then their current move in the same direction and thus IR and IB should have the same signage?

https://www.electricaltechnology.org/2014/09/delta-connection-power-voltage-current.html
Screenshot 2023-08-29 231047.png
 

Attachments

  • Screenshot 2023-08-29 231047.png
    Screenshot 2023-08-29 231047.png
    29.4 KB · Views: 102
Engineering news on Phys.org
Isn't it just a matter of convention? Picture clearly shows current directions. You could mark IB as going up, that would change all equations, giving IB+IR for L1 (that's assuming I understand correctly what L1 is).

That would also make the system of equations a bit chaotic to my taste though.
 
Borek said:
Isn't it just a matter of convention? Picture clearly shows current directions. You could mark IB as going up, that would change all equations, giving IB+IR for L1 (that's assuming I understand correctly what L1 is).

That would also make the system of equations a bit chaotic to my taste though.
How can phase shift of L1 be both IB+IR and IB-IR?
 
david90 said:
Regarding the picture below, the author calculates L1's current with KCL equation IR-IB = L1. Why is the KCL equation not IR+IB = L1
The author has clearly chosen the current polarities with the indicated arrows. That's why.

It can be an arbitrary choice, you may choose a different definition. But once the choice is made it must be followed.

There is no requirement that the defined current polarities match the voltage polarities. They can be defined separately, arbitrarily.
 
I agree with DaveE. In order to keep a more clear rule we take R as more than S and S more than T and the direction of current from S to R,from T to S and from R to T.
1693548033334.png
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...