The Dayton 2A562 Time Delay Relay operates with normally open contacts, meaning it remains inactive until the set time period of 3 to 60 seconds elapses, at which point the contacts close. However, it does not meet the user's requirement of running for a specified time and then shutting off. Instead, the user is advised to consider an "on delay" relay with normally closed contacts for the desired functionality. A suggested alternative is the Dayton 1EGB3 Relay, which can perform the needed operation. The discussion clarifies that the 2A562 will not fulfill the user's intended purpose.
Southerner
Messages
3
Reaction score
0
Can someone please tell about the Dayton 2A562 Time Delay Relay.
Does it wait 3 to 60 seconds before powering on, or does it wait 3 to 60 and then power off?
I am looking for something that will run for 3 to 60 seconds and then shut off.
thanks
 
Engineering news on Phys.org
Southerner said:
Can someone please tell about the Dayton 2A562 Time Delay Relay.
Does it wait 3 to 60 seconds before powering on, or does it wait 3 to 60 and then power off?
I am looking for something that will run for 3 to 60 seconds and then shut off.
thanks

did you do a google search ? there are many references

one I looked at stated it has a set of normally open contacts


Dave
 
Yes, but just because it says N.O. contacts that still doesn't answer the question of how the timer works-the the it's active or the time it waits before it's active...
 
Southerner said:
Yes, but just because it says N.O. contacts that still doesn't answer the question of how the timer works-the the it's active or the time it waits before it's active...

well from my understanding it does :)

it implies that the contacts are open (N.O. = normally open) till the time period set is reached and then the contacts close

Dave
 
I'm assuming what you want is the following: When input power is applied the load receives power. When the time interval has elapsed the load is switched off. When input power is removed the cycle repeats.

If the above is what you want then you can use an "on delay" with normally closed contacts. I don't think the solid state relays will do this. However, this mechanical one will:

http://www.drillspot.com/products/425611/Dayton_1EGB3_Relay

The 2A562 will not do what you want.
 
TurtleMeister said:
I'm assuming what you want is the following: When input power is applied the load receives power. When the time interval has elapsed the load is switched off. When input power is removed the cycle repeats.

If the above is what you want then you can use an "on delay" with normally closed contacts. I don't think the solid state relays will do this. However, this mechanical one will:

http://www.drillspot.com/products/425611/Dayton_1EGB3_Relay

THANKS! I knew one must exist like that...
 
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...