Can a DC-AC Inverter Work for Light Loads on an Alarm System?

  • Thread starter Thread starter CWatters
  • Start date Start date
  • Tags Tags
    Inverter Light
AI Thread Summary
A user seeks a solution for powering an alarm system with a UPS that struggles with light loads, causing noise interference with the alarm panel. The alarm operates on a 220VAC to 9VAC adaptor, and the user considers options like increasing the battery capacity or using a 12-13V DC feed, but these present challenges. The ideal solution is a 12V DC to 220V AC pure sine wave inverter that can handle loads from 0 to 50W, though such models are hard to find. An alternative suggestion is a 12V DC to 9VAC pure sine wave inverter, with recommendations for specific UPS models that cater to light loads. The discussion highlights the importance of finding a compatible inverter to avoid issues with harmonic-rich power sources affecting the alarm system.
CWatters
Science Advisor
Homework Helper
Gold Member
Messages
10,546
Reaction score
2,324
I have an alarm system that I would like to put on a UPS. Problem is the UPS that I've tried aren't very happy on the light load presented by the alarm. The power consumption is virtually zero unless the alarm is sounding. I think this is causing the UPS I have to generate a lot of noise that's messing with the alarm panel.

The panel operates from a 220VAC to 9VAC mains adaptor. I've looked at a few options such as increasing the battery capacity in the alarm panel itself and feeding the panel something like 12-13V DC (which should go through it's bridge rectifier) but these introduce other problems.

So what I'm looking for ideally is a 12V DC to 220V AC pure sine wave inverter that is stable on loads from 0 to say 50W. Do such things exist as I can't find one that specifically refers to light load operation.

An alternative would be a 12V DC to 9VAC pure sine wave inverter.
 
Engineering news on Phys.org
The class of UPS you need is called 'home network battery backup', like the BGE50/70/90 series.
I'm sure it exists for 220V too.
 
Pure sine is going to be expensive.

This el-cheapo inverter will be happy at light load. Here in US it's under twenty bucks at Walmart, surely there's a 220 volt version in your country.
https://smedia3.webcollage.net/0144...WSLYKQ&Signature=DBWkz5FQCSQVUd3V1+LODFnYkvo=

If the problem is in your alarm panel, ie it's intolerant of a harmonic-rich power source, this inverter won't do your job. A snip from the manual:

upload_2017-3-11_8-29-9.png
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...