Delta connected load

  1. Apr 3, 2013 #1
    A balanced 3 phase load is rated at S=10KVA and 500V. The device is operating at 90% nominal voltage and 100 % line current.

    The question is:
    if the load is delta connected, find the phase current in per unit and SI units.

    I calculated correctly that the per unit line current value is 0.58 pu, but the answer given for Ip=6.7A and I don't see why.

    I calculated S=VI* S/V=I*=20A and 6.7 is 20/3......I thought that for delta connected load, you Iphase=Iline/√3..... I am out by a factor of 1/√3 please explain!
     
  2. jcsd
  3. Apr 3, 2013 #2
    Also can anyone explain why delta connection produces 1/3 of the instantaneous power given the same Z and V?
     
Know someone interested in this topic? Share this thread via Reddit, Google+, Twitter, or Facebook