Determine Transformer KVA output and Power Factor

AI Thread Summary
The discussion focuses on calculating the KVA output and power factor of two transformers, T1 and T2, operating in parallel under a lagging power factor of 0.8. The impedances of the transformers are given as Za=0.04+j0.09 and Zb=0.01+j0.07, both rated at 3000 KVA. The user attempts to determine the KVA output for each transformer but encounters an error in their calculations, resulting in a total output of 3899 KVA, which is incorrect. Clarification is sought on the formula Za/(Za+Zb), which represents the impedance ratio of transformer T1 to the total impedance of both transformers. Understanding this ratio is crucial for accurate load distribution and KVA output calculations.
maluzha
Messages
1
Reaction score
0
1. Two transformers T1 and T2 in parallel supply a common load at a lagging pf of 0.8, their per unit impedance are 0.04+j0.09 and 0.01+j0.07 at the same kva ratings of 3000KVA each and load power = 5500KVA

Determine the kva output of each transfromer and power factor

This is how i worked it:
Za=0.04+j0.09
Zb= 0.01+j0.07
Zt=0.05+j0.16

Za/(Za+Zb)= 0.048<66.04/0.168<72.65
=0.286<-6.61
Zb/(za+Zb)=0.071<81.86/0.168<72.65
=0.423<9.21
Sa=5500<-36.86*0.423<9.21 = 2326<-27.65
Sb= 5500<-36.86*0.286<-6.61 = 1573<-43.47

Sa+Sb gives a total of 3899kva which is wrong!
 
Last edited:
Physics news on Phys.org
Za should be .098<66.04

Why is it Za/(Za+Zb) don' understand this part.

Thanks
 
Za/Za+Zb is the ratio of Za to the total load
 