Determining a heat pump's yearly energy output

AI Thread Summary
To estimate a heat pump's yearly energy output for a building, start by calculating the total heat loss at the coldest outdoor design temperature and the internal heat gain. The difference will indicate the heat required on the coldest day. Next, determine the lowest temperature at which the heat pump can fully heat the building, and analyze local outdoor temperature history. By calculating the heat needed and the heat provided by the heat pump across varying temperatures, you can sum these values to ensure they meet the building's annual energy requirement of approximately 80,000 kWh. Accurate insulation details and temperature variations are crucial for precise calculations.
TSN79
Messages
422
Reaction score
0
A building needs a certain amount of energy during a year (kWh) for room heating. An air to water heat pump has been installed to provide heat to a radiator system (55/40°C). How do I go about estimating how much of the yearly energy need the heat pump will cover? What confuses me is that the outside air temperature varies from -15 to +20°C during the year, and I don't know how to consider that variable. Not that I would know what to do if the outside temperature was fixed :frown: Does one usually use some average yearly temperature? Could anyone provide som basic procedures here? Thank you!
 
Engineering news on Phys.org
TSN79 said:
A building needs a certain amount of energy during a year (kWh) for room heating. An air to water heat pump has been installed to provide heat to a radiator system (55/40°C). How do I go about estimating how much of the yearly energy need the heat pump will cover? What confuses me is that the outside air temperature varies from -15 to +20°C during the year, and I don't know how to consider that variable. Not that I would know what to do if the outside temperature was fixed :frown: Does one usually use some average yearly temperature? Could anyone provide som basic procedures here? Thank you!
The quality of the insulation in the building walls and roof will be a major factor, as well as what kind of doors are used for ingress and egress (assuming no windows get opened). Do you have any information on the building insulation?

I'll page @russ_watters to get a better reply for you...
 
berkeman said:
Do you have any information on the building insulation?
Not really, but that kind of information has gone into a calculation that sombody else has already done, resulting in a total energy need over a year (for room heating) of about 80 000 kWh.
 
A basic procedure:
1) Calculate total heat loss at the outdoor "design temperature", the typical coldest outdoor temperature.
2) Calculate the internal heat gain.
3) The difference is how much heat is needed to heat the building on the coldest day.
4) The OP implies that the heat pump will not provide the amount of heat calculated in step 3. If so, calculate the coldest temperature at which the heat pump will fully heat the building.
5) Find the outdoor temperature history for your area.
6) Calculate the heat required, and the heat provided by the heat pump, for the range of temperatures from the coldest day to coldest temperature at which the heat pump provides 100% of the heat.
7) Add up the results. The total heat from the heat pump, plus the additional heat needed on the coldest days, should add up to about 80,000 kWh. If so, you are done. If not, start over.
 
TSN79 said:
How do I go about estimating how much of the yearly energy need the heat pump will cover?
I don't understand. Why don't you think the answer is simply, "all of it"?
 
How did you find PF?: Via Google search Hi, I have a vessel I 3D printed to investigate single bubble rise. The vessel has a 4 mm gap separated by acrylic panels. This is essentially my viewing chamber where I can record the bubble motion. The vessel is open to atmosphere. The bubble generation mechanism is composed of a syringe pump and glass capillary tube (Internal Diameter of 0.45 mm). I connect a 1/4” air line hose from the syringe to the capillary The bubble is formed at the tip...
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
I'd like to create a thread with links to 3-D Printer resources, including printers and software package suggestions. My motivations are selfish, as I have a 3-D printed project that I'm working on, and I'd like to buy a simple printer and use low cost software to make the first prototype. There are some previous threads about 3-D printing like this: https://www.physicsforums.com/threads/are-3d-printers-easy-to-use-yet.917489/ but none that address the overall topic (unless I've missed...
Back
Top