Difference in material between 1250A, 40KA & 1250A, 50KA?

In summary, a high power busbar will need to have more rigid construction to handle the forces produced by fault current. This will add to the cost of the busbar and breakers. Sometimes a current limiting inductor is used to reduce the cost of the busbar and breakers downstream.
  • #1
moh abdelsalam
2
0
At M.V. (10.5KV), what is the difference in material between 1250A, 40KA busbar & 1250A, 50KA?
 
Engineering news on Phys.org
  • #2
hi and welcome to PF :smile:

your question is extremely vague
What material ?
outline more clearly what you are referring to with as much relevant info as possible :smile:
 
  • Like
Likes moh abdelsalam
  • #3
davenn said:
hi and welcome to PF :smile:

your question is extremely vague
What material ?
outline more clearly what you are referring to with as much relevant info as possible :smile:
I'm sorry, I'm talking about busbar material (the conductor, insulation, supports and etc...).
 
Last edited:
  • #4
Here's some busbar information. This seems to be for more typical busbars and may not be as useful for high power applications. Still, most of the same problems will still need to be solved.

For high power AC systems, lots of engineering work will need to be done. The electrical characteristics will depend on geometry. Typically these will be large hollow roundish metal structures. Aluminum alloys are a popular choice, but has some concerns about mechanical/electrical connections.

After the electrical characteristics are determined, structural problems need to be solved.

This is a specialized field and you may need to hire a power engineer with experience with station/substation design if you need specifics.
 
  • Like
Likes moh abdelsalam
  • #5
One of the design considerations is rigidity.
Under high current faults the conductors are attracted to one another,
wirefor.gif
so it is required they be stout enough that a downstream fault will not make them bend and touch between supports which would cause another fault.

So i'll assume your 40 and 50 ka numbers are fault current ratings,beyond the 1.25 ka.
Presumably the busbar is supported as necessary and made more rigid considering the forces produced by fault current. Those forces are in proportion to the product of the currents as indicated in that Hyperphysics image above, http://hyperphysics.phy-astr.gsu.edu/hbase/magnetic/wirfor.html

502/402 = 1.56+,
ie 56% more bracing required.

That of course raises the cost of busbar and breakers.

Sometimes you'll see a current limiting inductor in switchgear.
It limits fault current allowing use of less expensive busbar and breakers downstream . My plant had them in the 4kv switchgear , located between the breakers supplying multi-thousand horsepower motors and those feeding only multi-hundred horsepower motors.
 
  • Like
Likes davenn and FOIWATER

Related to Difference in material between 1250A, 40KA & 1250A, 50KA?

1. What do the numbers 1250A, 40KA and 1250A, 50KA represent?

The numbers 1250A, 40KA and 1250A, 50KA represent different electrical ratings for a circuit breaker. The first number, 1250A, refers to the maximum current the circuit breaker can handle in amperes. The second number, 40KA or 50KA, represents the maximum short circuit current, or the amount of current that can flow through the circuit in the event of a fault or short circuit.

2. What is the difference between 40KA and 50KA?

The difference between 40KA and 50KA is the maximum short circuit current that the circuit breaker can handle. A circuit breaker with a 50KA rating can handle a higher amount of short circuit current than one with a 40KA rating. This means it can protect against larger faults or short circuits.

3. How does the short circuit current affect the choice of circuit breaker?

The short circuit current is an important factor in choosing the right circuit breaker for a specific application. A higher short circuit current rating is needed for larger electrical systems or equipment that can produce a higher amount of current. It is important to choose a circuit breaker with a rating that can handle the expected short circuit current to ensure safety and proper functioning of the electrical system.

4. Can a circuit breaker with a 1250A, 50KA rating handle a lower short circuit current?

Yes, a circuit breaker with a 1250A, 50KA rating can handle a lower short circuit current. The rating indicates the maximum amount of short circuit current it can handle, but it can also handle lower currents without any issues. It is important to choose a circuit breaker with a rating that is suitable for the expected short circuit current, but it can handle lower currents as well.

5. Are there any other factors to consider when choosing a circuit breaker?

Yes, there are other factors to consider when choosing a circuit breaker, such as the type of circuit, the voltage level, and the type of load. Different types of circuits and loads may require different circuit breaker ratings. It is important to consult with a qualified electrician or engineer to determine the appropriate circuit breaker for a specific application.

Similar threads

Replies
10
Views
2K
  • Electrical Engineering
Replies
3
Views
1K
  • Electrical Engineering
Replies
8
Views
343
Replies
2
Views
703
Replies
2
Views
4K
  • Electrical Engineering
Replies
5
Views
1K
  • Electrical Engineering
Replies
1
Views
674
Replies
5
Views
1K
  • Electrical Engineering
Replies
1
Views
817