Distance relay - impedance characteristic question

Click For Summary

Discussion Overview

The discussion revolves around the impedance characteristics of distance relays used for transmission line protection, particularly focusing on the interpretation of the second quadrant in the impedance plane and its implications for relay operation and directionality.

Discussion Character

  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant, Pauls, questions the meaning of the second quadrant in the impedance characteristics, suggesting it indicates negative resistance.
  • Another participant references an application note, suggesting that the second quadrant is inductive and relates the sign of resistance to the direction of power flow.
  • Pauls expresses confusion about the implications of bidirectionality in relays, questioning the necessity of two relays if the relay can operate in both directions.
  • A different participant proposes that the mathematical model indicates bidirectionality and mentions the potential addition of restraint coils.
  • One participant suggests consulting industrial training manuals for more detailed discussions on relay operation.
  • Another participant notes that the torques in the device are proportional to the RMS currents squared, implying that the basic device would be bidirectional.

Areas of Agreement / Disagreement

Participants express differing views on the implications of the second quadrant and the bidirectionality of relays, indicating that multiple competing interpretations remain unresolved.

Contextual Notes

There are limitations in the discussion regarding assumptions about relay operation, the definitions of impedance characteristics, and the mathematical models referenced, which are not fully explored.

nettub
Messages
2
Reaction score
0
Dear all!

I have a question about the impedance characteristics in the distance relay used for transmission line protection. I understand that in the first quadrant we have a inductive load and in the fourth quadrant we have a capacitive load. I, however, do not understand what we measure in the second quadrant that I marked red. We would have a negative resistance. Can someone please help me with that?

https://dl.dropboxusercontent.com/u/3809800/impedance_characteristics.jpg

Thanks,
Pauls
 
Last edited by a moderator:
Engineering news on Phys.org
Thanks for your answer.

That's what I thought and I also saw the paper. That means, however, that the relay is bi-directional. For me that's contradicting since the diagonal shown in my picture marks the operating direction of the relay. So when you want to detect both directions you would need 2 relays anyways. That means the -R and +X area would be redundant.
 
i think they're saying the math works out to a function that'd be bidirectional

there's discussion later on about adding restraint coils

i'm not a relay guy, just have watched over the shoulders of some genuine ones.

i'd resort to a genuine industrial training manual for in-depth discussions of how it's done in the real world..
http://www.pdfslibfree.com/applied-protective-relaying-westinghouse.pdf
http://www.osinerg.gob.pe/newweb/uploads/GFE/eventos/EVENTO%207/TEXTO%207A.pdf
 
Last edited by a moderator:
  • Like
Likes   Reactions: dlgoff
  • Like
Likes   Reactions: dlgoff
Since the torques are in proportion to RMS currents squared, it looks to me like the basic device would be bidirectional...
 

Similar threads

Replies
24
Views
3K
Replies
33
Views
4K
Replies
1
Views
2K
  • · Replies 5 ·
Replies
5
Views
5K
  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 9 ·
Replies
9
Views
3K
  • · Replies 31 ·
2
Replies
31
Views
9K
  • · Replies 11 ·
Replies
11
Views
4K
  • · Replies 15 ·
Replies
15
Views
5K