Hi,
Silly little question about the transformer short circuit test.
When I perform it with the secondary shorted and I get Req = Power / current2

is this Req = Rpri + Rsec?
If I measured Rpri and Rsec with a multimeter?

Thanks
 
Engineering news on Phys.org
tim9000 said:
is this Req = Rpri + Rsec?
It is Rpri+Rsec*(Npri/Nsec)2.
The second term on the RHS is the reflected secondary resistance or the secondary resistance "seen" by primary.
 
cnh1995 said:
It is Rpri+Rsec*(Npri/Nsec)2.
The second term on the RHS is the reflected secondary resistance or the secondary resistance "seen" by primary.
Can we move this a = (Npri/Nsec)2 term to get the primary and secondary resistances as seen by themselves?
So if I measure Rpri and Rsec with a multi meter then will the value of Rpri I get on the meter be
Rpri = Req - Rsec*(Npri/Nsec)2

Where Rsec is the value of the secondary from the meter?
 
tim9000 said:
Can we move this a = (Npri/Nsec)2 term to get the primary and secondary resistances as seen by themselves?
So if I measure Rpri and Rsec with a multi meter then will the value of Rpri I get on the meter be
Rpri = Req - Rsec*(Npri/Nsec)2

Where Rsec is the value of the secondary from the meter?
Yes (provided the test is performed with secondary shorted).
 
cnh1995 said:
Yes (provided the test is performed with secondary shorted).
Just to be 100% clear: When you say the test I presume you mean the Short Circuit test in finding Req, and not measuring the coils resistance with the multimeter? (because I can't see how it would make any difference to that)
So bottom line is that other than the values I can derive from Short Circuit and Open Circuit tests, I still need either the Primary coil resistance, or the Secondary coil resistance (via multimeter) to accurately and specifically know every individual parameter of the transformer? (i.e. to separate the primary and secondary resistance values out from Req)
Thanks again
 
tim9000 said:
Just to be 100% clear: When you say the test I presume you mean the Short Circuit test in finding Req, and not measuring the coils resistance with the multimeter? (because I can't see how it would make any difference to that)
So bottom line is that other than the values I can derive from Short Circuit and Open Circuit tests, I still need either the Primary coil resistance, or the Secondary coil resistance (via multimeter) to accurately and specifically know every individual parameter of the transformer? (i.e. to separate the primary and secondary resistance values out from Req)
Thanks again
Yes to all.
 
  • Like
Likes   Reactions: tim9000
cnh1995 said:
Yes to all.
Thank you