Efficient Cable Calculation for Urgent Motor Circuit - Help Needed

AI Thread Summary
The discussion revolves around calculating the appropriate cable size for a motor circuit with specific parameters, including a motor power of 0.37kW and a nominal current of 0.8 A. The user has calculated a target current of 1.5 A based on Bahraini regulations but is uncertain about the suitability of a 2.5mm cable, which has a higher current rating than needed. Concerns are raised about the voltage drop calculation, which exceeds the acceptable limit. Participants emphasize the importance of understanding local regulations and installation methods, suggesting that consulting a qualified local electrician is essential for compliance. The user is urged to review their training materials for further guidance on cable calculations.
walidabid
Messages
1
Reaction score
0
Good afternonn,
these are the motor and circuit data:

Motor power: 0.37kW,
Nominal current: I= 0.8 A
voltage: 415 V,
cable length = 80m
ambiant temperature: 50°C
Maximum voltage drop percentage =415*4% =16.6V

According to the Bahraini Regulations:
- temprature factor= 0.89
- core factor (3core cable)= 0.7

This is the calculation I did:
- target current=I/(0.89*0.7)=1,29A ==> 1,5A
when I check the current rated table, the suitable cable section will be 1.5mm but our contractor us a 2.5mm cable (I must verify his choice and prove that it's correct and submit the calculation to our consultant at least tomorrow morning!)

According to the current rated table, we get:
for the cable section: 2.5mm ==> current rating= 33A and Voltage drop /amp/m= 16

but when I calculate the Voltage drop /amp/m for my circuit, I find:
mV= dV*1000/(target current *L)= 16.6V*1000/(1,5A*80m) = 138,33mV >16 (from the table)

Now, what I have to do?
I don,t know how to proceed and finalize the calculation!

I have to make the verification for 20 different equipments with power variying between 0.37 and 48A!
Would you please help me and show me how to continue with the remainder calculation?

Your help is extreamly needed, I'am really blocked.
Thank you

Walid ABID
 
Engineering news on Phys.org
Walid ... your persistance is impressive how many more forums have you posted on?

Like I've mentioned before key to starting a cable calc for an inductive load is knowing what device you are going to protect the cable with as it will have to be able to cope with the inrush of the motor, having said that this is a very small motor and reduces that concern.
Secondly, regulations vary and unless one is knowledgeable of the bahraini electrical Reg's its thus a hard question to answer, we would need a copy of the regions electrical regs to attain the values to be applied.

Third and final you haven't stated what your cable type is nor its installation method, you have just given us values that you provide, we cannot confirm these without knowing you haven't made a mistake.

I assume you must be qualified to be requested to do this, if so you will have done this in your training and i recommend you review your notes or college books.

I can only re-iterate what i said before in that you need to discuss this with a local electrician who has knowledge of local rules and regulation, your tolerances in calcs may be tighter or more liberal than our (UK)... Hope you can appreciate how arkward trying to answer you question is, had you been UK base or even EU then it would have been a quick reply and full explanation.
 
If this calculation needs to be done to local codes, then we cannot help you here. Thread is closed.
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Back
Top