Electrical distribution sysytem

AI Thread Summary
Touching one phase of a 11kV/230V delta/star connected distribution transformer with an ungrounded neutral can result in an electric shock due to the distributed capacitance of the other phases to earth. The current experienced may vary, potentially reaching a fraction of an amp, which could be significant enough to feel or even be lethal. When a person touches a phase, they create a parallel path with the distributed capacitance, affecting voltage levels across the phases. The IEEE standard 241 recommends grounding the neutral with a resistor to mitigate shock risks. Understanding the distributed capacitance and its effects is crucial for safety in electrical distribution systems.
G.natarajan
Messages
3
Reaction score
0
in 11kv /230 v delta /star connected distribution transformer neutral not connected to earh,then if we touch the one phase (ex:R phase)of secondery line, shall we get shock or not?
 
Engineering news on Phys.org
Yes.

The circuit is completed by distributed capacitance of other two phases to earth.
Current might amount to goodly fraction of an amp.
Or it might be too little to feel.
 
jim hardy said:
Yes.

The circuit is completed by distributed capacitance of other two phases to earth.
Current might amount to goodly fraction of an amp.
Or it might be too little to feel.
Thanks.i am new to this forum.
 
G.natarajan said:
Thanks.i am new to this forum.
Dear
If the ground is neutrely charged .
And if The phase line is positively charged.
The distribution Transformer neutrel not grounded. Then we touch the line
From standing the ground what happens, will get full shock.
 
Full shock ? no.

There is capacitance from all the wires and equipment in your distribution system to earth. How much depends on the size of the system.
Currents flow through that capacitance from each phase to earth.

When everything is balanced those three currents add to zero, of course .

When you grab a phase you place yourself in parallel with one of those distributed capacitances.
So voltage across that one drops and the others rise.
How much current flows ? I'd say maximum would be 230V/Xc
natalyat.jpg


There might be a little contribution from interwinding capacitance in the 11kv/230v transformer.
I've measured around 0.3 amp on a 480 system in a power plant.
That'd be a good shock and might be lethal but it wouldn't cause an explosion.
IEEE standard 241"The Green Book" recommends the neutral be earthed with a resistor approximately equal to Xc.
A good industrial reference book will have formulas to estimate distributed capacitance.
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...