Equilibrium Point: Does Internal Variable Input Need to be Zero?

  • Thread starter Thread starter tuebingen78
  • Start date Start date
  • Tags Tags
    Equlibrium Point
AI Thread Summary
The discussion centers on the concept of equilibrium points in control systems, specifically whether the internal variable input must be zero. An example is provided with a heating element in water, where the system reaches equilibrium when heat loss equals heat input, maintaining a constant temperature. It is noted that an equilibrium point can also occur when no input is applied, though this is considered trivial. The role of negative feedback in restoring a system to equilibrium is emphasized. Overall, the equilibrium point is crucial for understanding system stability and response.
tuebingen78
Messages
2
Reaction score
0
or some time the single point, in control systems they say it is the point where the internal variables of the system never change .

my question if we must have input of system zero, or it can be any value?

thanks
 
Engineering news on Phys.org
If you had a small heating element in a large container of water, (so the water didn't boil) the heater would heat the water until the losses due to convection, conduction and radiation equalled the power being added to the system by the heater.

At that stage, the water temperature would remain the same. This would be called an equilibrium point.

If you did nothing and didn't turn on the heater, that would also be an equilibrium point but a trivial one which you would not normally consider.
 
Equilibrium point also refers to the point that a system is restored to by negative feedback.
Bob S
 
Bob S said:
Equilibrium point also refers to the point that a system is restored to by negative feedback.
Bob S

thanks for your answer, but can you explain more or give a reference for this.
 
tuebingen78 said:
thanks for your answer, but can you explain more or give a reference for this.
Look at the first two pictures and equations for inverting and non-inverting op amps in this:
http://www.rfcafe.com/references/electrical/opamps.htm
In both cases, the gain of the differential op-amp is very high (G > 10,000), and the gain drops out of the equation. Derive these equations using

Vout = G(Vin+ - Vin-)

The op-amp output drives the feedback circuit to the point where the voltage at both inputs are equal (equilibrium).
Bob S
 
Last edited:
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...
Back