Homework Statement
10kVA, 200:400 V transformer gave these test results:
open circuit test (LV winding supplied): 200 V, 3.2 A, 450 W
short circuit test (HV winding supplied): 38 V, 25 A, 600 W
Homework Equations
Calculate the efficiency when the transformer delivers its rated kVA at 0.85 power factor lagging.
3. The Attempt at a Solution
Calculated in part a of the question:
Open Circuit
Rc = V2/P = 2002/450 = 88.9ohms
S = VI = 200 x 3.2 = 640VA
Q = sqrt(6402 - 4502) = 455VAR
Xm= V2/Q = 2002/455 = 87.81ohms
Short Circuit
Rt = P/I2 = 600/252 = 0.96ohms
Zt = V/I = 38/25 = 1.52ohms
Xt = sqrt(1.522 - 0.962) = 1.178ohms
Referring to LV side
Rt' = 0.96(200/400)2 = 0.24ohms
Xt' = 1.178(200/400)2 = 0.295ohms
Part b
Efficiency = Power out / Power in
Power out = S x pf = 10000 x 0.85 = 8500W
Power in = 8500W + copper loss + iron loss
Copper/winding loss, Pc = I2 x Rt' = 252 x 0.24 = 150W
Iron/core loss, Pi = V2/Rc = 382/88.9 = 16.24W
Efficiency = Power out / Power in = 8500/(8500+150+16.24) = 98.08%
Need help to check the calcution in red. anyone?