Finding the value of a neutral earthing resistor

Click For Summary
SUMMARY

The discussion focuses on calculating the suitable value of a neutral earthing resistor for an 11 kV motor connected via switchgear. The phase impedance is specified as 0.3 + j0.3 ohm, and the Earth return path resistance is 0.42 ohm. The goal is to ensure that the voltage rise at the motor during an Earth fault does not exceed 430 V. The calculations indicate that the required neutral resistance should be approximately 6.16 ohms after considering the existing circuit impedances.

PREREQUISITES
  • Understanding of electrical impedance and resistance calculations
  • Knowledge of Earth fault analysis in electrical systems
  • Familiarity with complex numbers in electrical engineering
  • Proficiency in using Ohm's Law and related equations
NEXT STEPS
  • Study the principles of Earth fault protection in high voltage systems
  • Learn about impedance calculations in electrical circuits
  • Research the impact of neutral earthing resistors on system stability
  • Explore methods for measuring Earth fault loop impedance
USEFUL FOR

Electrical engineers, power system designers, and technicians involved in high voltage installations and fault analysis will benefit from this discussion.

Neil Hayes
Messages
15
Reaction score
2

Homework Statement



An 11 kV motor is fed by cables from a transformer via switchgear,
having a phase impedance of 0.3 + j0.3 ohm. The Earth return path to
the transformer neutral has a resistance of 0.42 ohm. Determine a
suitable value of neutral resistance if the voltage rise at the motor in the
event of an Earth fault at the motor is not to exceed 430 V. Neglect
transformer winding resistance.

Homework Equations

The Attempt at a Solution



Hi there everyone. This is a question that I'm working on at the moment. My attempt so far is as follows. Maybe someone can tell me if I'm on the right path?
[/B]
Well using the information given the fault current would be 6350/.42 = 15121 amps

The 6350 here is the phase voltage.

To meet the requirement in the question the current would need to be reduced to
430/.42 = 1023.8 amps

Using an Earth path impedance of 6350/1023.8 would give 6.20 ohms

What I'm thinking of doing next is R = the square root of Z² - X²

This gives me 6.19 ohms and we already have .3 ohms in the circuit so we would need to add a resistor of value 6.16 ohms.

Would this be correct?

Any help would be greatly appreciated!

Neil
 
Last edited:
Physics news on Phys.org
Hello again everyone!

I'm actually just looking at the question there again and think that I made a mistake. I thought that the .42 ohms was the impedance but I think that the impedance from the transformer to the motor is Z = 0.3 + j0.3 which is .42 but I think that the Earth return path to the transformer neutral is also .42 ohms which would give me an Earth fault loop impedance of Z = 0.72 + j0.3.

Does that make more sense I wonder?
 

Similar threads

  • · Replies 13 ·
Replies
13
Views
3K
  • · Replies 2 ·
Replies
2
Views
1K
  • · Replies 12 ·
Replies
12
Views
5K
  • · Replies 6 ·
Replies
6
Views
19K
Replies
1
Views
7K
  • · Replies 10 ·
Replies
10
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
1K
  • · Replies 9 ·
Replies
9
Views
7K
  • · Replies 12 ·
Replies
12
Views
2K