Engineering Fundamentals ofElectric circuits

AI Thread Summary
The discussion revolves around calculating the required capacitance to improve the power factor of a load drawing 10 kVA at a power factor of 0.8 lagging to 0.9 lagging. The initial apparent power is 10 kVA with a real power of 8 kW. To achieve the desired power factor, the reduction in reactive power must be determined, which involves finding the voltage across the source under the initial conditions without a capacitor. The solution requires understanding the relationship between apparent power, real power, and reactive power. Ultimately, the necessary capacitance can be calculated once the reactive power and source voltage are established.
Kokuson
Messages
4
Reaction score
0

Homework Statement



The load in Fig. 11.44 draws 10 kVA at PF =0.8
lagging. If |IL |=40 A rms, what must be the value of C
to cause the source to operate at PF =0.9 lagging?

Homework Equations



P(apparent power VA)= |I| |V| cos@
@ = @V - @I
cos@= p.f
X= Xrms*(2)^0.5
S(complex power)= 0.5 * I * V (cos@ - j sin@)

The Attempt at a Solution


I just face a difficulty in knwoing the face of IL
I will be thankful if you solved the wole problem.
 

Attachments

  • Ele204.gif
    Ele204.gif
    11.8 KB · Views: 451
Physics news on Phys.org
First, there is no capacitor. And, you have 10 kVA at 0.8 so 8 kW.

You add a capacitor and you get 10 kVA at 0.9 and 8KW

Find the reduction in the reactive power required to make the pf equal to 0.9. To find the capacitor value now you have its reactive power and you need voltage which is equal to the voltage across the source.

You can find the voltage across the source using the initial condition when there is no capacitor.
 