Fuse Breaking Current: Explained

  • Thread starter Thread starter adool_617
  • Start date Start date
  • Tags Tags
    Current Fuse
AI Thread Summary
The minimum breaking current is the lowest current that can cause a fuse to disconnect, which is typically higher than the fuse's rated current. For example, if a fuse is rated at 10 A with a minimum breaking current of 15 A, it will not trip if the current is between these values. Continuous current flow at 13 A, which exceeds the rated current but is below the minimum breaking current, will not cause the fuse to disconnect. It is crucial to select a fuse that operates outside this range to ensure proper protection. Understanding these parameters is essential for safe electrical system design.
adool_617
Messages
13
Reaction score
0
Dear all , i have an important question which i need answer for it , if you look at a catalog for fuses you will find the fuse rated current which for example is 10 A

and you will find a value called minimum breaking current and it is usually higher than the rated current for our example let's say about 15 A

so what is meant by minimum breaking current , does it means the fuses will not disconnected
unless a value higher than or equal 15 A which is higher than the normal rated current .

and what will happen if a continuous current flow for a long time with value 13 A which is higher than the rated current and smaller than the minimum breaking current

please help

thanks
 
Engineering news on Phys.org
Low test current (I1) is defined as; the largest current the fuse can hold for one hour without breaking.
High test current (I2) ; the lowest current which breaks the fuse within one hour.

Not quite sure what minimum breaking current is, but i believe it must be I2. Not sure though, someone else might know.

If you se a graph like http://www.buildingdesign.co.uk/elec-technical/hager-t1/18-hager-4.gif" . I1 is 1.13A and I2 is 1.45A in a 1A fuse.
 
Last edited by a moderator:
well , actually after doing some search i found this:
the minimum breaking current is the minimum current that can cause the fuse to disconnect
for example assume the normal current for a fuse is 10 A and the minimum breaking current is 15 A , so between this region the fuse cannot completely trip or disconnect so when you choose the fuse you must make sure that you are not going to work in this region .
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Back
Top