Will a Failed Breaker Cause a Generator to Lose Residual Magnetism?
A synchronous generator retains some residual magnetism even when the regulator power supply is disconnected, allowing it to generate a small voltage. Concerns arise if the engine shuts down while the main breaker fails to trip, potentially leading to a loss of residual magnetism and preventing the generator from starting up again. Unlike induction motors, which can lose magnetism when stopped under load, synchronous generators typically maintain their magnetism unless specific conditions are met. The use of a shunt trip breaker is recommended for monitoring various fault conditions beyond just overcurrent. Proper management of the generator's operation is crucial to avoid damaging the starter during a failure scenario.
Josh111
I plan to use a automatic genset controller to protect/run a synchronous generator. This controller determines when to disconnect the starter by determining the generator frequency. I plan to connect the exitor regulator to the main breaker so when the main breaker trips the regulator is shut down. Any fault condition will trip the breaker and also shut down the engine. It is my understanding that even with the regulator power supply disconnected there is still some residual magnetism in the rotor which causes the generator to still generate a small voltage.
My concern is about what would happen if the engine shuts down and the breaker fails to trip, causing the load to still be connected to the generator as it slows down. Will this cause the generator to lose it's residual magnetism thus causing it to not generate at the next startup which would cause the starter to never disengage thus damaging it?
I am aware that if an induction motor is stopped while a load is applied it will lose it,s magnetism causing it to need manual remagnetisation upon next startup. I am not sure if it applies the same to my application with a syncronous generator.
Any confirmation of any answers will be nice!
There are Demagnetizing effects in electrical machine as a magnetizing system which involved to induction phenomenon if secondary current load exist, similar what where happen in transformers.
Hi Josh,
Sure enough, a frozen contactor can make things messy when you need to go offline. Personally, I'd put fuses in a set of series for such an emergency. Fuses are a pain, but they're reliable - not something you can say about many breakers.
As for the magnetization, that happens with dyno-type generators, but the world doesn't use those much, except for welding machines. When the rotor gets its polarity reversed, or the user wants to reverse it, you have have to expose the commutator and apply a stout current (a car battery is good) to the brushes in order to reverse the polarity (while it's still!).
As for an induction motor, they don't have a permanent field. Same's true with your synchronous generator.
Remember that your synchronous generator will become a synchronous motor if you attempt to turn off the engine with the generator on line!
Mike
I do not plan to run generator online with grid.
As far as the contactor/breaker goes, I plan to use a shunt trip breaker because I am monitoring for faults other than just overcurrent. A simple fuse will not just work in my application. I am monitoring voltage and frequency as well as other conditions. A fault will trip the shunt trip breaker.
I thought that a synchronous generator had residual magnetism otherwise it would be necessary to introduce a voltage at each startup.
The site below says that an induction generator can be self excited if capacitors are present and that the residual magnetism is what starts the induction
process.www.qsl.net/ns8o/Induction_Generator.html
Sorry I was not clear earlier.
Wow,
That's an odd one. Back in the 70's, people were using induction motors as online generators, but my understanding was that you had to have the online voltage to ensure rotor magnetization - otherwise, it's output would die down.
As for the capacitors, back then, they were there for power factor correction.
Admittedly, I'm having difficulty wrapping my head around around this problem... For my own edification, I'd like to see how it turns out.
Best Wishes,
Mike
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...