Ground clearances for transmission lines

Click For Summary

Discussion Overview

The discussion revolves around the reasons for large ground clearances for 765 kV transmission towers. Participants explore various factors influencing tower height, including electrical safety, environmental conditions, and the physics of electric fields. The conversation touches on theoretical, practical, and safety considerations related to high voltage transmission lines.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Conceptual clarification

Main Points Raised

  • Some participants question why ground clearances are so large, suggesting that calculations based on arc length do not fully explain the height of towers.
  • It is noted that the voltage affects the separation of wires and the length of insulators, with higher voltages requiring greater distances to maintain safe electric field gradients.
  • Factors such as conductor sag during high temperatures, ice loading, sway in high winds, and nearby trees are mentioned as considerations for ground clearance.
  • Some participants express confusion about the relationship between voltage increase and tower size, seeking clarification on the physics behind this correlation.
  • There are mentions of the effects of environmental conditions like rain, fog, and salt spray on clearance calculations.
  • One participant shares an anecdote about experiencing voltage differences while parked under high voltage lines, raising concerns about electric field induction.
  • Discussion includes the impact of contaminants in the air on breakdown fields and the implications for safety during faults, such as lightning strikes.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the exact reasons for the large ground clearances or the calculations used to determine them. Multiple competing views and uncertainties remain regarding the influence of various factors on tower height and safety.

Contextual Notes

Limitations include the dependence on specific environmental conditions, the complexity of electric field interactions, and the variability in standards across different regions. Some assumptions about the effects of EMFs and the conditions under which shocks may occur are also unresolved.

lagrangman
Messages
13
Reaction score
2
Why are ground clearances so large for 765 kV towers?

I did a little research on this and even if the switching surge factor is 3 and you have a factor of safety of 1.5, in air (3 kV/mm), it corresponds to 1.62 m of maximum arc length, which doesn't explain why towers are so large.

According to "Power System Analysis and Design," by J. Duncan Glover et al., "Line height is selected to satisfy prescribed conductor-to-ground clearances and to control ground-level electric field and its potential shock hazard."

From what I have read the effect of low frequency EMFs on humans is pretty minimal. Has anyone actually been shocked by a power line 10 m away? If so, can someone explain the physics behind this? Does anyone know the calculation the NESC committee uses to come up with minimum clearances?

Thanks a lot.
 
Engineering news on Phys.org
The voltage you have calculated determines the separation of the wires and the length of the insulators.

The current and magnetic field in a balanced 3-PH line sums to zero, as does the electric field. The fields induced in the Earth are minimised by making the towers high relative to the wire separation. The wires swing in the wind and sometimes carry an ice load.

But what happens during a fault, say when a phase is shorted to ground by lightning during a rainstorm ?
 
Ground clearance also has to factor in sag when conductor temperature is highest, sag when ice loaded, sway of conductors and the nearest trees in high winds, snow depth, and the possibility of vehicles driving underneath.

Rain, fog, or salt spray in the air may also modify the calculations.

Also, as @Baluncore mentioned, there is the issue of line-to-ground fault currents.

All these considerations are not unique to 765 KV. I also suspect (but I'm not sure) that IEEE standards for clearance are uniform worldwide and not customized to local conditions such as salt spray or snow pack.
 
  • Like
Likes   Reactions: berkeman
Thanks for the help, but I am still confused. I used 765 kV as an example, since I live in California and there are no 765 kV lines due to the size. My main question is why does an increase in voltage correspond to a massive increase in transmission tower size?

As for when one line is shorted to ground in a rainstorm, that would be dangerous even at 4 kV.

For sagging in extreme weather, I assume that that would also be similar at 230 or 500 kV.

For arcing in weather, do you know the dielectric strength of humid, salty air?

I also assume that the main concern is the electric field perpendicular to the line, since magnetic field depends on current. Also if EMFs were a huge concern, wouldn't you see a lot linemen with cancer, which I haven't heard about.
 
anorlunda said:
snow depth
Good point! I never thought of that, but I can see how that would be a big factor for the transmission line paths through the Sierras and other places that get a significant snow pack.

https://image.shutterstock.com/image-photo/image-450w-42107338.jpg
1572368643276.png
 
lagrangman said:
My main question is why does an increase in voltage correspond to a massive increase in transmission tower size?
For all the reasons mentioned before. Volts per meter is the gradient of concern. More volts needs more meters to hold the V/m ratio constant. But there are also minimum heights for low voltage lines, so constant V/m might not hold for them.

@berkeman , this crossing always stands out in my mind. It seems shockingly low. It is Skyline Drive in Shenandoah National Park, a mountain ridge. The mountain slope is 30-45 degrees. In the foreground is a 115 KV line and behind is a 230 KV line. Vehicles up to 12 feet tall drive on that highway. Maybe snow blowers too.
1572374021575.png


1572374073616.png

1572374378385.png
 
  • Wow
Likes   Reactions: berkeman
Yeah, volts-per-meter at the ground can be a concern. Many years ago a few of us went out in the California desert to see the new Solar Power plant. We decided to drive up one of the surrounding hills to get a good overview and take some photos.

We parked under some high voltage transmission lines and got out of the car. We soon noticed that the car and us were at different voltages. Not a lot, probably a few hundred volts and, fortunately, a very low current (at least thru our shoes, we didn't try barefoot!).
 
  • Wow
  • Like
Likes   Reactions: berkeman and anorlunda
lagrangman said:
Why are ground clearances so large for 765 kV towers?

I did a little research on this and even if the switching surge factor is 3 and you have a factor of safety of 1.5, in air (3 kV/mm), it corresponds to 1.62 m of maximum arc length, which doesn't explain why towers are so large.

According to "Power System Analysis and Design," by J. Duncan Glover et al., "Line height is selected to satisfy prescribed conductor-to-ground clearances and to control ground-level electric field and its potential shock hazard."

From what I have read the effect of low frequency EMFs on humans is pretty minimal. Has anyone actually been shocked by a power line 10 m away? If so, can someone explain the physics behind this? Does anyone know the calculation the NESC committee uses to come up with minimum clearances?

Thanks a lot.
When transmission voltages are deep in EHV region and start approaching UHV ballpark then the answer is YES: you can be shocked even at that distance from power line when touching bigger insulated conductive objects or simply by touching grounded objects. E-field induction can be quite serious when massive boundled conductors and very high AC voltages are employed...
 
  • Like
Likes   Reactions: anorlunda
Tom.G said:
We parked under some high voltage transmission lines and got out of the car. We soon noticed that the car and us were at different voltages. Not a lot, probably a few hundred volts and, fortunately, a very low current (at least thru our shoes, we didn't try barefoot!).
Might be a good time to mention Step-Potential.

step-potential.jpg

image compliments of
https://www.esgroundingsolutions.com
 
  • Like
Likes   Reactions: anorlunda
  • #10
Also it wouldn't hurt to mention that 3 kv/mm figure (refered to by OP as breakdown field for normal air) is good only for small air gaps with uniform field. Average breakdown field in wire-plane and wire-wire gap configuration is much lower than that. Especially for positive surges in very long air gaps.
 
  • Like
Likes   Reactions: dlgoff and anorlunda
  • #11
zoki85 said:
Especially for positive surges in very long air gaps.
Correct. Also especially with contaminants in the air. Salt spray. Rain. Smoke and ashes. Snow blower fountain.
 
  • Like
Likes   Reactions: dlgoff and zoki85

Similar threads

  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 7 ·
Replies
7
Views
7K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 17 ·
Replies
17
Views
6K
  • · Replies 6 ·
Replies
6
Views
6K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 2 ·
Replies
2
Views
9K
Replies
2
Views
2K
  • · Replies 9 ·
Replies
9
Views
13K