Ground Grid Study: Short Circuit Current Analysis

Click For Summary
SUMMARY

The discussion centers on the short circuit current analysis for a ground grid study at a substation for a wind farm, specifically questioning the use of the high side short circuit current of 6.399kA instead of the larger low side current of 26.825kA. The rationale provided indicates that the high voltage line's ground rise potential must be minimized, making the high side current more relevant for the ground grid study. Insights from an electrical utility professional suggest that ground resistance studies focus on minimizing risks associated with high voltage lines contacting the earth.

PREREQUISITES
  • Understanding of short circuit current calculations
  • Familiarity with substation design and transformer configurations (wye/wye)
  • Knowledge of ground resistance testing methodologies
  • Basic principles of SCADA systems in electrical utilities
NEXT STEPS
  • Research IEEE Std 1050-1996 for ground grid design standards
  • Learn about short circuit current analysis techniques in substations
  • Explore ground resistance measurement methods and their applications
  • Investigate the implications of ground rise potential in high voltage systems
USEFUL FOR

Electrical engineers, utility professionals, and anyone involved in substation design and ground grid studies will benefit from this discussion.

tr0ypayne
Messages
2
Reaction score
0
Short Circuit Current

Hi,

I am reviewing a ground grid study of a substation for a wind farm that is being built. The ground grid will be for a substation with a low side of 34.5kV and two transformers that step the high side voltage up to 345kV. There are six distribution feeders on the low side coming from the wind farm generation and the step up transformers are wye/wye. My question is why was the short circuit current (6.399kA) of the high side used on the ground grid study and not the low side current (26.825kA)? Is this correct? I would think the load side short circuit current would be used since it is larger.

Can any of you give me some insight into this?

Thanks,

Troy
 
Last edited:
Engineering news on Phys.org
Hi tr0ypayne and welcome to PF.

I'm really no expert here but I did work for an electrical utility for a number of years. When we did ground resistance studies we would take resistance readings from the ground grid to points at varying distances out and along the transmission line. The idea was that if the high voltage line should make contact with the earth, ground rise potential would be minimized. (the low side potential is low enough as to not be the major problem) I worked with the SCADA side of the utility and these studies were required by the telco so that high currents didn't get into their system.

You might want to PM M.S.J as he seems to know a lot about power transmission.
Here's his profile page: https://www.physicsforums.com/member.php?u=84682"

Hope this helps a little.

Edit: Here's an ipaper that might be of interest.
http://www.scribd.com/doc/11358767/IEEE-Std-10501996"
 
Last edited by a moderator:
Thanks for your help and thoughts. I will send M.S.J. a message. And I am also looking forward to talking to you again when I have a SCADA question.

Thanks again.
 

Similar threads

Replies
9
Views
2K
  • · Replies 13 ·
Replies
13
Views
6K
  • · Replies 32 ·
2
Replies
32
Views
4K
Replies
80
Views
5K
  • · Replies 4 ·
Replies
4
Views
5K
Replies
4
Views
4K
  • · Replies 8 ·
Replies
8
Views
3K
Replies
31
Views
8K
  • · Replies 11 ·
Replies
11
Views
2K
Replies
12
Views
8K