jim hardy said:
As I've said i never spent any time around BWR's , just walked through one once.
I went by this report, which is an analysis and re-thinking of station blackout scenarios done around 1981. They used Brown's Ferry's design as their case study. I stumbled across it while following events at Fukushima on another forum. It's been posted here at PF back in 2011.
http://www.ornl.gov/info/reports/1981/3445600211884.pdf
I'm not a BWR guy.
If you are one, you are certainly more versed than i in their station blackout approach . old jim
First off, amazing reference. I'm always looking for gems like that to add to my little collection.
The problem is the station blackout scenario is only a 4~8 hour scenario. I fully agree with their approach of keeping RCIC online, as you can bypass RCIC interlocks and run it down to about 45 psig, and by keeping the reactor close to depressurized you have the ability to immediately transition to shutdown cooling the moment it becomes available again (typical SDC interlocks are around 145 psig).
Another quick note about the normal 4-8 hour station blackout scenario. The acceptance criteria is power being restored in that 4 or 8 hour timeframe, the reactor being brought to cold shutdown, and the suppression pool temperature not exceeding some arbitrary limit (in the range of 175F +/- 15). The other main reason you want to keep vessel pressure low, is that as the suppression pool heats up, you have less capability for the pool to absorb the energy during a reactor blowdown, which can result in containment failure if a LOCA occurred during the event. By keeping pressure low, you can have much higher suppression pool temperature limits, and also prevent containment failure in the event a blowdown or LOCA occurs towards the end of the event. (note: Mark 3 and possibly mark 2 containments don't have an issue here, as it is my understanding that they can survive the entire SBO coping time without violating their suppression pool temperature limits)
The issue though, is the relief valves for BWRs utilize air accumulators and DC solenoids. The total air accumulator supply for all SRVs is usually enough for about 30 lifts against design containment pressure. There are backup air bottles, however you can always have a situation where these are unable to restore pressure to the instrument air system due to damage (it is non-safety grade for some obscure reason), or worse, you don't have DC/AC power in the right places to open the valves and bypass the interlocks on the instrument air system.
If you are in an extended situation where you do not have DC power (Fukushima had no DC power at the start of the event in units 1 and 2, and limited in 3), or if you have to do more than a few dozen SRV lifts and deplete your accumulators, you will lose the ability to use SRVs to control vessel pressure. This is where the extended scenario departs from the normal station blackout scenario. The SRVs are manual staged valves, and are either open or shut. To maintain vessel pressure at 100 PSI requires operators to be opening and closing these valves manually, depleting the air supply in them and exhausting your DC power supply.
Further complicating the event is the fact that RCIC's operation is dependent on the suppression pool as a heat sink. If you are in an extended situation, and you blowdown early, you introduce a large volume of heat to the pool, and limit how long RCIC can operate. RCIC is self cooled, and once suppression pool water passes 200F you start to wear the bearings and can fail the pump. Furthermore, as vessel pressure decreases, and drywell/containment pressure increases, you get less dP over the RCIC turbine which results in less injection to the vessel. I should note that heatup of the suppression pool was likely one of the direct causes of the RCIC system failing at Fukushima unit 2 (ran for 70 hours).
The strategy the plant I'm at is taking, is recognizing the extended blackout event, stripping all non-essential loads and shutting down a full safety division of DC power, cross tieing the various DC power busses to the RCIC system to ensure continued injection and automatic flow control, keeping the vessel pressurized. We will actually declare 10CFR50.54(x) to violate our HCTL (heat capacity temperature limit) on the suppression pool in order to keep utilizing RCIC and keep injecting to the core. Once we either restore power, or get portable pumps going, we will cool the suppression pool via "feed and bleed". Once the pool is cooled below the HCTL again, we will do a reactor blowdown by taking portable batteries and directly wiring them up to the SRV terminal blocks and transition to cooling the reactor using portable pumps using the suppression pool -> reactor -> relief valves -> suppression pool loop (alternate shutdown cooling), and either feed and bleed or portable pump setups to cool the suppression pool.
The scenario changes if you are at an isolation condenser plant like dresden or oyster (it changes greatly at oyster as they don't even have a HPCI...ONLY IC and LP corespray). ICs buy you more time, and allow use of engine driven pumps, provided you can get it started properly and identify its function (one of the Fukushima unit 1 flaws, operators were not well trained on the system). Oyster, provided their ICs are in service and portable pumps or the on-site diesel driven pumps are available, is probably in the best shape for extended SBO, as you are essentially injecting against atmosphere and can keep cooling as long as there is enough decay heat for natural circulation (likely days).