Heat at plug end of power cord higher than rest of cord

  • Thread starter Thread starter FactChecker
  • Start date Start date
  • Tags Tags
    Heat Power Rest
Click For Summary

Discussion Overview

The discussion centers on the phenomenon of the plug end of a vacuum cleaner's power cord becoming warmer than the rest of the cord during operation. Participants explore potential causes, including the quality of connections and the physical condition of the cord, while considering implications for appliance safety and functionality.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant observes that the plug end of the cord gets warmer than the rest, questioning whether this indicates a defect at the plug end.
  • Another participant inquires if the plug itself gets hot, suggesting that the thickness of the plug's plastic might conceal heating.
  • A participant notes that the issue persists even when using a heavy gauge extension cord, indicating a potential problem at the vacuum plug end.
  • One contributor proposes that a bad connection between the vacuum and the plug could create resistance, leading to heating as current flows, and provides a hypothetical example of how even a small resistance could result in significant heat generation.
  • Another participant agrees with the idea of a bad connection and mentions that connections are never perfect, implying that some heating is expected depending on the current.
  • One participant shares a general observation that similar heating occurs in many high-power appliances, attributing it to contact resistance between the plug and socket, and notes that crimped connections may also contribute to increased resistance.

Areas of Agreement / Disagreement

Participants express varying hypotheses about the cause of the heating, with some suggesting a defective cord or connection while others acknowledge that some heating is typical. No consensus is reached on a definitive cause.

Contextual Notes

Participants mention the possibility of resistance in connections and the physical condition of the cord, but do not provide specific measurements or detailed assessments of the cord's integrity.

Who May Find This Useful

Individuals interested in electrical safety, appliance maintenance, or troubleshooting electrical connections may find this discussion relevant.

FactChecker
Science Advisor
Homework Helper
Messages
9,449
Reaction score
4,717
In running my vacuum cleaner, I have noticed that the plug end of the cord gets warmer than the rest of the cord. Since the wire gauge and current must be the same through the entire length, why would this happen? I have noticed this regardless of the wall socket that I use and it doesn't seem like the wall socket gets hot. Does it imply that the vacuum cleaner cord is defective at the plug end? Perhaps I should test if it still happens when a heavy gauge extension is used and see if any part warms up.
 
Engineering news on Phys.org
Does the plug itself get hot?
 
CWatters said:
Does the plug itself get hot?
Not that I can tell. It just seems to be the first foot or so of cord. But the plug plastic is thicker, so that might hide heating there. I tested it in a large capacity extension cord and it warms up at the vacuum plug end, not at the wall socket. I can only think of one possible reason: a bad cord at that end. I will see if I can notice that behavior in other high watt appliance cords.
 
Last edited:
If there is a bad connection between the vacuum and the plug there will be some resistance there. The high resistance of the connection will heat up as the vacuum cleaner draws current. You could have something as low as a 1 Ohm connection and this would be a problem. If your vacuum cleaner draws about five amps then you would essentially have a 25 Watt heater in the cord. There would only be a 5 Volt drop so your vacuum would still operate.

This is a common enough problem that there is an entire industry dedicated to using IR cameras to find bad connections in industrial settings. The idea is to catch problems by looking for high heat in equipment. That way you can repair it before it fails.

Does the cord look like it was pinched or severely bent anywhere? Your cord should be made of braided wire. It might be hanging by a thread inside the insulation.
 
  • Like
Likes   Reactions: anorlunda and FactChecker
Aaron Crowl said:
If there is a bad connection between the vacuum and the plug there will be some resistance there. The high resistance of the connection will heat up as the vacuum cleaner draws current. You could have something as low as a 1 Ohm connection and this would be a problem.
This confirms my suspicion that there must be a problem at that end of the cord. I was wondering if I might be overlooking something about heating in a good cord, but I guess not.
This is a common enough problem that there is an entire industry dedicated to using IR cameras to find bad connections in industrial settings. The idea is to catch problems by looking for high heat in equipment. That way you can repair it before it fails.
Interesting.
Does the cord look like it was pinched or severely bent anywhere? Your cord should be made of braided wire. It might be hanging by a thread inside the insulation.
No. It looks fine. But I am going to assume that there is something wrong at the plug end, cut off that end, and replace the plug.
Thanks.
 
It depends on how warm. Connections are never 100% perfect and will always heat depending upon how much current is passing.
 
  • Like
Likes   Reactions: FactChecker
This is something I have noticed on most high power appliances. I just assumed that it was the contact resistance between the plug and socket. Also many cords are crimped inside. They will also have an increased resistance at that point.

BoB
 
  • Like
Likes   Reactions: dlgoff, jim hardy, berkeman and 1 other person

Similar threads

Replies
2
Views
3K
  • · Replies 17 ·
Replies
17
Views
4K
  • · Replies 20 ·
Replies
20
Views
7K
  • · Replies 17 ·
Replies
17
Views
3K
  • · Replies 79 ·
3
Replies
79
Views
7K
Replies
14
Views
12K
Replies
6
Views
4K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 8 ·
Replies
8
Views
6K