Heat exchange in active system

Click For Summary
SUMMARY

The discussion focuses on calculating the necessary water flow rate to cool a 200-liter tank by 10 degrees Celsius using a coiled copper pipe. The inlet water temperature is 20 degrees Celsius, while the water in the coil enters at 50 degrees Celsius, flowing at approximately 3 liters per second. The calculations reveal that to maintain a constant temperature in the tank, a cooling flow rate of 1.2 liters per second is required, based on the heat capacity of water and the thermal properties of copper. The participant also considers the impact of coil length and tank size on system efficiency.

PREREQUISITES
  • Understanding of heat transfer principles
  • Familiarity with thermal conductivity of materials, specifically copper
  • Knowledge of fluid dynamics, particularly flow rates
  • Basic proficiency in performing thermal calculations using specific equations
NEXT STEPS
  • Research "Heat transfer calculations for fluid systems"
  • Study "Thermal conductivity of copper and its applications"
  • Explore "Fluid dynamics principles in cooling systems"
  • Investigate "Optimizing geothermal cooling systems for efficiency"
USEFUL FOR

This discussion is beneficial for engineers, geologists, and anyone involved in designing or optimizing cooling systems, particularly those utilizing geothermal or water-based methods.

paullom
Messages
2
Reaction score
0
I am trying to calculate the amount of water that would have to pass through a 200 litre tank (water inlet temp is 20degrees c) in order to cool water by 10degrees in a closed loop (in a coiled copper pipe) suspended in the tank the coil has a total length of 30 lineal m and a diametre of 20mm the water in the coil enters at 50 degrees and is traveling at approximately 3 litres per second. I am a geologist not a physician and this has me stumpt. Any help or advise would be much appreciated.
 
Science news on Phys.org
It’s been a while since I did these sorts of sums but..

For the temperature in the tank to be constant the power entering must match that extracted so first work out the power in Watts (=Joules/second) entering the tank via the hot coil using:

Heat capacity of water = 4180 J/Kg/K
Temperature drop (10 K)
Mass of water per second (3kg/S)

= 4180 * 10 * 3
= 125,400 J/S
= 125 kW

So that's how much has to be removed by the cold water flow.

Quick check that the coil is big enough. Last time I did this I used this equation:

Dt = (P * Wt)/(A * C)

Where

Dt = average delta T across wall of pipe in Centigrade
C = thermal conductivity of copper = 401 W•m−1•K−1
Wt = wall thickness in meters? Assume 2mm = 0.002m ?
A = area of pipe wall in meters = Pi * 0,02 * 30 = 1.88sqm
P = Power in watts

Dt=(125*10^3 * 0.002)/(1.88 * 401)
=0.33K

So can assume no temperature drop across wall of copper pipe (unless it scales up!)

Incoming hot is 50C, require 10C drop so it leaves at 40C. Average 45C

Lets assume water temperature of the tank is maintained at 45C.

Temperature rise of cooling water is 45-20C = 25C

Flow rate required is

= 125,400/(4180 * 25)
= 1.2L/Sec

Note that it will come out colder than required until the tank is upto temperature. that might take quite awhile.
 
Thanks a lot for that.
It all make sense to me and is far simpler than I thought. I think I will play with the variables to see if I can improve the effeciency and size etc of the system. I am using this to try and build a ground water cooled refrigerant system.

Re the calc for the suitability of the coil length if i change the parameters at what point do you think that the temperature drop across the pipe is of any concern to the whole system?

Does the size of the tank have any bearing on any of this, or is it as I suspect that it will only vary the time it takes for the tank to reach the average water temp.

Again thanks a bunch.
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 56 ·
2
Replies
56
Views
6K
  • · Replies 15 ·
Replies
15
Views
4K
  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
1
Views
3K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 4 ·
Replies
4
Views
3K