Hi all, I have a 90kva 3 phase 440volt/220volt stepdown

  • Thread starter Thread starter spider2127
  • Start date Start date
  • Tags Tags
    3 phase Hi Phase
Click For Summary

Discussion Overview

The discussion revolves around the behavior and measurements of a 90kVA 3-phase 440V/220V step-down transformer, particularly focusing on voltage readings between phases and ground when the transformer is under no load. Participants explore the implications of these readings and the potential issues related to phase unbalance and measurement techniques.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Experimental/applied

Main Points Raised

  • One participant reports voltage readings of 150V, 104V, and 150V from each phase to ground when the transformer is not loaded, questioning whether this indicates a fault in the transformer.
  • Another participant challenges the meaningfulness of the voltage readings to ground when the secondary is not connected, asking for clarification on the setup.
  • A participant suggests that the readings may be influenced by the connection of one phase to ground through a switchboard, leading to unbalanced measurements when disconnected.
  • There is a recommendation to use a less sensitive analog meter for more accurate readings, as high-impedance digital multimeters (DMMs) may produce misleading results due to their sensitivity.
  • Participants discuss the commonality of issues arising from high-impedance meters and suggest alternative measurement methods, including using a lightbulb instead of a meter.
  • One participant shares their experience with using low-tech meters for practical work, emphasizing their effectiveness over high-precision instruments in certain situations.
  • Another participant mentions having a similar meter with a high voltage range but lacks appropriate test leads, contributing to the discussion about measurement tools.

Areas of Agreement / Disagreement

Participants express differing views on the validity of the voltage readings and the implications for the transformer. There is no consensus on whether the transformer is faulty, and multiple perspectives on measurement techniques and their effectiveness are presented.

Contextual Notes

Participants highlight potential limitations in measurements due to the nature of the equipment used and the setup of the transformer, including the influence of grounding and the characteristics of the meters employed.

spider2127
Messages
2
Reaction score
0
Hi all, I have a 90kva 3 phase 440volt/220volt stepdown transformer.
When i test on no load ie secondary not connected to anything but the power is on,
i get 220v between phases but to Earth or ground i get
1st phase 150volts
2nd phase 104volts
3rd phase 150volts
Does this mean my transformer is U/S due to phase unbalance
 
Engineering news on Phys.org


Well if the secondary truly is not connected to anything at all then how can you expect any meaningful reading between a 'phase', and I think you mean 'leg', and ground? So tell us exactly what is hooked up.
 


sorry yes one leg and ground. Ok i have a 3phase 440v/220v tranny that when connected to mulitple switchboards i get a reading of 155v red to ground,4v white to ground and 153v blue to ground. When i disconnect main switchboard and have nothing connected to the tranny my voltages from each leg to ground are as above
 


i bet you're using a pretty good meter, maybe a DMM.

Try a real cheap analog one that's just a couple thousand ohms/volt.
sometimes low-tech works best.
 


Does the transformer have a star point that you connected to ground? Otherwise, what Averagesupernova said applies. The voltages are floating, your measurements are meaningless. Don't throw the transformer away. :smile:
 


when connected to mulitple switchboards i get a reading of 155v red to ground,4v white to ground and 153v blue to ground. When i disconnect main switchboard and have nothing connected to the tranny my voltages from each leg to ground are as above


Draw yourself an imaginary circle around the transformer, like a fence..
That fence represents the insulation of the transformer.

When you connect a voltmeter from one transformer phase to earth, you let a trickle of current flow out of transformer, through meter and over your fence into earth.

Apparently one of your switchboards connects white phase to earth.
So you get solid readings then, the meter current returns to transformer from earh via white phase.

But -How does that meter current get back into transformer when you've disconnected white phase from earth? How can it jump the fence?

It can't.
That's why you get flakey unbalanced readings, only a fraction of your meter current finds its way back over the fence. Insulation is imperfect and your meter is too sensitive.

Use a less sensitive meter and you'll read nearly zero on all three phases.

Or use a lightbulb instead of a meter.

it's a common problem ever since high impedance DMM's became so popular.
Typical DMM is 10 meg input.
Simpson 260 is i think 5Kohm/volt on AC, so on 250 volt scale = 1.25 meg.

A 1 kohm per volt el cheapo meter is what you need for that measurement.
Check the little yellow $ 9.95 GE analog meter at Walmart.


old jim
 
Last edited:


Jim Hardy: Have you experienced the strange looks from people that I have when you tell them a low-tech cheap meter is still necessary?
 


Averagesupernova said:
Jim Hardy: Have you experienced the strange looks from people that I have when you tell them a low-tech cheap meter is still necessary?

indeed.

I do 95% of my work with the $9.95 meter, even have an external resistor to make a 15 volt scale for automobile work. I soldered nice long test leads with alligator clips to it(nice Meuller copper ones) , because the cheapies are too short and fall out.

My high accuracy Fluke DMM is wonderful on rare occasions one needs precise resolution, maybe three times a year around the house.

When i retired the guys gave me a caricature drawn by the office wag portraying me in my old hat carrying a Simpson 260 and analog oscilloscope. With those two instruments you can fix anything.
 


I have something similar to a 260 except it has a 3000 volt or higher range I believe. I don't have any test leads that fit it though. At least they didn't draw you with a pair of dry-cells taped around a door-bell.
-
Edit:
CORRECTION: It is a Triplett with a 6000 volt range.
 
Last edited:

Similar threads

  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 19 ·
Replies
19
Views
4K
Replies
4
Views
11K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 12 ·
Replies
12
Views
5K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 7 ·
Replies
7
Views
5K
  • · Replies 16 ·
Replies
16
Views
4K
  • · Replies 21 ·
Replies
21
Views
7K