Open-circuit tests on transformers primarily reveal excitation losses rather than I²R losses because there is no load applied during the test. The current measured in this scenario is the magnetizing current, which is typically small for quality transformers. If a reference material fails to mention the small magnitude of magnetizing current, it may be an oversight by the author. However, it is important to note that magnetizing current is not always negligible and can vary depending on the transformer. Understanding these nuances is crucial for accurate analysis of transformer losses.
aaqeel123
Messages
1
Reaction score
0
hi guys, i was studying on transformers losses, i need help in some problems.

why open-circuit test show only excitation losses and not i2R losses..

thanks...
 
Physics news on Phys.org


What reference are you referring to that seems to ignore copper losses?
 


think about that for a moment

what is magnitude of current in open circuit test?

just magnetizing current 'cause there's no load on transformer...
which for a quality transformer should be small (though not zero)
and when you express it as a fraction of rated current and square that it gets even smaller


so if your text did not state that the magnetizing current is small enough to ignore then it was an error of omission by the author,

and it is not always the case that magnetizing current is negligible...
 