How Do I Calculate the Required Kvar for a 22KW Motor?

AI Thread Summary
To calculate the required KVAR for a 22KW motor, the no-load current is essential, which is 10 amperes in this case. Taking 90% of the no-load current gives 9 amperes, suggesting that a 6 KVAR capacitor, which can handle this current, is suitable. However, there are concerns about the voltage assumptions, as a 6 KVAR capacitor at 9A implies a supply voltage of 667V, which may not be accurate. Clarification on the phase voltage and whether the motor is three-phase is necessary for accurate calculations. Using the three-phase power formula, the calculated power aligns closely with the motor's rating, confirming the approach.
ssana
Messages
13
Reaction score
0
Dear all,

I have one 22KW motor.
I want to know how much Kvar i need to install for it.
According to my information, i need to check no load current of motor (it is taking 10 ampere at no load), and than take 90% of no load current (90% of 10 ampere is 9 ampere), so install capacitor that can take maximum 9 ampere current (6 kvar capacitor takes 9 ampere current).
So 6 Kvar is suitable to install in 22KW motor.
Am i calculating in correct way?
 
Last edited:
Engineering news on Phys.org
I can't help with your question, but I was looking at your figure of 9A for 6kVAR. This implies a supply voltage of 667v. Perhaps I am not doing this right.

This is a 3 phase motor, is it? Maybe that 6kVAR is a set of capacitors drawing 2kVAR per phase? Seems an odd way to rate it, if it is, summing the phases. But the figure of 2kVAR at 9A would give a phase voltage of 220v which might be more likely.

So what is your phase voltage there?

Do you have a table of kVAR vs. current for power factor correction capacitors? If so, do the kVAR figures all turn out to be exact multiples of 3?
 
Dear NascentOxygen,
Using three phase formula,
Power = Voltage x Current x √3
Power = 380V x 9A x 1.732
Power = 5923 VA
OR
Power = 5.923 KVA
Approximately 6 KVA

Hope that this will helpful to you.
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...