How Do You Determine Pumping Power for a Homemade Water Chiller?

  • Thread starter Thread starter tectactoe
  • Start date Start date
  • Tags Tags
    Power
AI Thread Summary
To determine the appropriate pumping power for a homemade water chiller, it's essential to calculate the total head loss, which includes both the vertical lift and the friction losses in the piping. The head loss due to bends, such as 90-degree elbows, can be significant and should be factored into the overall calculation. Using the formula P=(rho)*(g)*(h) provides a theoretical minimum head, but additional losses from pipe friction must also be considered. A larger pipe diameter can reduce friction losses, making it easier to achieve the desired flow rate without requiring an excessively powerful pump. Ultimately, a balance between pump size, cost, and efficiency is crucial for optimal performance.
tectactoe
Messages
38
Reaction score
0
I have a heat pump water heater that cycles the refrigerant in reverse, thus using the cooling portion of the evaporater to chill the water rather than to heat it (basically, a 50-gal storage homemade chiller).

The problem is, I need to circulate the water throughout the tank, or else all of the chilled water will sit near the bottom.

There's an opening/valve near the bottom of the tank (normally used for space heating I believe, not sure) and the tank inlet isn't being used - so there's my recirc path. But the path will contain some bends and twists since the valve is at the bottom pointed one way and the inlet is on the top pointed another way. Also, the pipe will probably need to reroute a little to accomidate the place where I'll screw in the pump to the outside of the tank.

So that's my question - I'm going to use a pump to recirc the water. But how powerful of a pump do I need? I know it has to overcome the head in the pipe - but how exactly do you figure that out?

I'll be using copper pipe with a given diameter and I'll be able to measure the length/height of the set up... I know bends and vertical lifts contribute to loss, but how, exactly? I don't want to get a pump that won't do the duty, but I don't want overkill either.

Thanks, guys and gals.
 
Engineering news on Phys.org
I wouldn't think you'd need much at all, maybe a little aquarium pump or something. Calculating the head is as easy as P=(rho)*(g)*(h), so that gives you your minimum theoretical head needed not taking into account piping losses.
 
Yeah, I know the pump will be a very small one... I'm actually more worried about getting a pump that's way too big, (cost issues, etc). so if I can calc pressure loss from (rho*g*h), how do piping losses factor in? Looking at the tank, I'm probably going to need about four 90 degree elbows in there. Just as well, does the copper pipe friction supply any kind of reasonable loss?

I know these elbows and such may not provide losses significant enough in my specific case, but I'm to the point now where I'm just downright curious and would like to know how to account for these other losses.

Thanks for your help
 
The loss depends on the velocity through the pipe, so if you have a big enough pipe, you won't need to worry about it. You can look up a pipe friction calculator online to size the pipe.
 
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Thread 'What's the most likely cause for this carbon seal crack?'
We have a molded carbon graphite seal that is used in an inline axial piston, variable displacement hydraulic pump. One of our customers reported that, when using the “A” parts in the past, they only needed to replace them due to normal wear. However, after switching to our parts, the replacement cycle seems to be much shorter due to “broken” or “cracked” failures. This issue was identified after hydraulic fluid leakage was observed. According to their records, the same problem has occurred...
Back
Top