Heat pump performance varies significantly between northern and southern climates due to differences in outside temperatures. In southern climates, the average coefficient of performance (COP) is higher at 19.54 when the outside temperature is 5°C, compared to a lower COP of 9.77 in northern climates at -10°C. For two identical houses maintaining an indoor temperature of 20°C, the power ratio required to heat the northern house versus the southern house is approximately 0.5, indicating that the northern house requires significantly more energy. The discussion highlights that heat loss rates may not be strictly linear and depend on factors like temperature difference and heat loss mechanisms. Understanding these dynamics is crucial for optimizing heat pump efficiency in varying climates.
sapiental
Messages
110
Reaction score
0
1. North vs. South. A heat pump is designed for southern climates extracts heat from the outside air, and delivers air at 20C to the inside of the houses. What is the average coefficent of performance of the heat pump: (Consider this to be a Carnot device)

a) In the south where the average outside temperature is 5C?
b) In the north where the average outside temperature is -10C?

c)Two Identical houses, one in the north and one in the south, are heated by this pimp, and maintain indoor temperatures of 20C. Considering heat loss through the walls, windows, and roof, what is the ratio of the electrical powers required to heat the houses and to maintain the interiors at 20C. Express your result as P_n_/P_s_

a) K = T_h_/(T_c_-T_h_)

T_c_ = 5C + 273.15 = 278.15K
T_h_ = 20C + 273.15 = 293.15K

K = 293.15/(278.15-293.15)
= 19.54

b) K = T_h_/(T_c_-T_h_)

T_c_ = -10C + 273.15 = 263.15K
T_h_ = 20C + 273.15 = 293.15K

K = 293.15/(263.15K-293.15)
= 9.77

c) solving for P_n_

(9.77kWh)(3.6x10^6J)= 3.51x10^7 J/s

solving for P_s_

(19.54kWh)(3.6x10^6J)=7.03x10^7 J/s

P_n_/P_s_ = (3.51x10^7 W)/(7.03x10^7 W)

= .5


I would really appreciate it if someone reviewed my answeres. What confuses me is the line "Considering heat loss through the walls, windows, and roof". Did I miss plugging in a number somehwere, how do I calculate it? Or is it just theoretical?

Thanks a lot in advance!
 
Physics news on Phys.org
sapiental said:
I would really appreciate it if someone reviewed my answeres. What confuses me is the line "Considering heat loss through the walls, windows, and roof". Did I miss plugging in a number somehwere, how do I calculate it? Or is it just theoretical?

Thanks a lot in advance!
a) and b) appear to be correct. c) is simply stating that the heat pump is continually working to replenish heat lost. So the ratio of power consumed is a ratio of input work per unit time of one house compared to the other. Since:

\eta = \frac{Q_{out}}{W_{in}}

What is:

\frac{W_{in-n}}{W_{in-s}}?

I think you have to assume that Qout per unit time is the same for both (ie the heat is lost - and therefore replaced by the heat pump - at the same rate for both houses). You do not have enough information otherwise.

AM
 
Last edited:
is it

(3.6x10^6)/(2x3.6x10^6)

damn, again .5??

Correct me if I'm wrong but 9.77 = 9.77kWh (Q_out_) per 1 kwh (W_in_)

Thanks again.
 
sapiental said:
is it

(3.6x10^6)/(2x3.6x10^6)

damn, again .5??

Correct me if I'm wrong but 9.77 = 9.77kWh (Q_out_) per 1 kwh (W_in_)

Thanks again.
It is simply:

P_n/P_s = W_{in-n}/W_{in-s} = \frac{Q/\eta_n}{Q/\eta_s} = \frac{\eta_s}{\eta_n} = 2

AM
 
Andrew Mason said:
I think you have to assume that Qout per unit time is the same for both (ie the heat is lost - and therefore replaced by the heat pump - at the same rate for both houses). You do not have enough information otherwise.

AM
It occurs to me that the rate of heat loss for identical houses should be proportional to the temperature difference between the interior and exterior.
 
OlderDan said:
It occurs to me that the rate of heat loss for identical houses should be proportional to the temperature difference between the interior and exterior.
I agree that they won't have the same rate of heat loss, due to the difference in exterior temperatures. But I would think that the rate of heat loss might depend on the way the heat is lost: eg: radiation, convection or conduction. Would heat loss necessarily vary linearly with temperature difference?

AM
 
Andrew Mason said:
I agree that they won't have the same rate of heat loss, due to the difference in exterior temperatures. But I would think that the rate of heat loss might depend on the way the heat is lost: eg: radiation, convection or conduction. Would heat loss necessarily vary linearly with temperature difference?

AM
It probably would not be strictly linear, but I believe it is the usual assumption for defining R-Factor in construction. For example

http://esa21.kennesaw.edu/activities/rfactor/rfactor.pdf

The model assumes conduction with rate proportional to temperature difference.
 
I think they want you to assume the heat loss Q is proportional to the temp difference between the inside and outside of the house as the house has the same u value.ie heat loss per degree C. as it has the same resistance to heat loss as it is the "same house"
 